Right or wrong I purchased a 36' 6AWG 50 amp RV extension cord and cut it up to wire everything.
The sheath is embossed "For Recreational Vehicle Use 50 Amperes C(ETL)US 3126867 TYPE STW 600V FT-2 3/C 6AWG + 1/C 8AWG 60C"
US Wire and Cable says STW is Extra hard service cord. Thermoplastic constructed jacket. 600 volt, weather resistant for outdoor use.
Did you leave the existing plug on it?
Sent from my SM-G930V using Tapatalk
csheath
198
FL
I left the original male plug on a short piece I connected to my load bank. I used a piece without connectors to wire the breaker to the panel on the back of the house. Then I used repair connectors to make a cable to hook the generator to the house.
csheath
198
FL
So is this pretty much what will fix it besides the ground rod, bonding strap, and power cable?
http://www.homedepot.com/p/GE-50-Amp-Temporary-RV-Power-Outlet-U054P/100193650
That is what I used on the side of my generator.
The link supplied by DieselAddict would be a proper house side receptacle. I like the looks of this one better. http://www.homedepot.com/p/Reliance-Controls-50-Amp-Non-Metallic-Power-Inlet-Box-PBN50/205337810. You would also need to address the breaker size and wiring from the breaker to the receptacle. I recommend you have an electrician do that for you.
The Conntek 1450SS2-15 15-Foot Temporary Power Cord or similar would connect the two together if it's long enough for where you set the unit.
fpchief
220
South Alabama
I am seeing a lot of 3 wire plugs. And someone posted with a pic of a three wire. If I went with a three wire plug, what line is being lost? I know it has to have two hot going to two different terminals, so is the neutral being lost? Forgive my ignorance.
Daybreak
2 Star Admiral
761
Va
Howdy,
4 wires need to be connected to your house panel.
Bonding strap is to be disconnected on generator.
Wire of size, and circuit breaker of size.
Bmxenbrett
30
You cant use a 3 prong plug. You need both hot legs, a neutral and a ground. Its common to have a 4prong plug/outlet for an electric dryer. Im not sure what they offer in exterior 50a covers. Homedepot may not have what you are looking for so you may want to try a electrical supply house.
fpchief
220
South Alabama
Nice thread you have! I am with the family at disney so i was put on hold, but plan to be finished with it this weekend.
TheAlfredo
11
Miami, FL
I've never seen so much confusion on "grounding". You should only be using 1 ground at a time. Your house is grounded at at the service entrance. Since you are using an interlock and and breaker as your transfer switch, you are only opening both hot legs. Your Neutral is always connected to your generator and the rest of the house. Therefore you have to use the ground in your cord connected to the house. You leave the bonding strap in place at the generator and DO NOT add a grounding rod.
DieselAddict
1,956
Efland, NC
Per code if you are wired up with a 4-wire setup and the neutral is bonded in the main panel at the service entrance, you need to remove the bonding jumper at the generator.