Hello All!
I have an 803A with roughly 2000 hours on it. It runs regularly. During use one day, it ceased to send power to the breaker panel it’s hooked up to. After investigation, I saw the green AC Interrupter light was off and would not come back on. The unit is not hooked to anything that can pull more than 75% load, so no way it could have overloaded. My spare 803A is working just fine on the same circuit. I’ve gone through many of the threads on this forum and can’t seem to narrow it down. Short of buying some high dollar parts such as overload relays, I'm hoping I've missed something simple. Here’s the general situation:
No Load at Lugs, AC Circuit interrupter light will not come on when S5 switch turned to CLOSED.
The circuit interrupter light, DS7, has been tested and works correctly. The Circuit Interrupter switch, S5, has been tested and functions correctly. Voltage tested on switch S5 when running indicates 24 volts at S5-2 & S5-3, however S5-5 only shows 2 volts….? My understanding is S5-5 should have 24 volts also. This traces all the way back to TB5-16 I believe and shows 2V there as well.
K1 Relay has been replaced with brand new unit.
K15 Relay replaced with brand new relay.
Hertz Gauge is registering at 60HZ.
Voltage Gauge is indicating 240V.
Convenience receptacle tests with meter to 120V. Confirmed with power tool the convenience receptacle works as intended and the generator is producing power. Just not sending it to the lugs.
Thank you in advance!
I have an 803A with roughly 2000 hours on it. It runs regularly. During use one day, it ceased to send power to the breaker panel it’s hooked up to. After investigation, I saw the green AC Interrupter light was off and would not come back on. The unit is not hooked to anything that can pull more than 75% load, so no way it could have overloaded. My spare 803A is working just fine on the same circuit. I’ve gone through many of the threads on this forum and can’t seem to narrow it down. Short of buying some high dollar parts such as overload relays, I'm hoping I've missed something simple. Here’s the general situation:
No Load at Lugs, AC Circuit interrupter light will not come on when S5 switch turned to CLOSED.
The circuit interrupter light, DS7, has been tested and works correctly. The Circuit Interrupter switch, S5, has been tested and functions correctly. Voltage tested on switch S5 when running indicates 24 volts at S5-2 & S5-3, however S5-5 only shows 2 volts….? My understanding is S5-5 should have 24 volts also. This traces all the way back to TB5-16 I believe and shows 2V there as well.
K1 Relay has been replaced with brand new unit.
K15 Relay replaced with brand new relay.
Hertz Gauge is registering at 60HZ.
Voltage Gauge is indicating 240V.
Convenience receptacle tests with meter to 120V. Confirmed with power tool the convenience receptacle works as intended and the generator is producing power. Just not sending it to the lugs.
Thank you in advance!