Guys, thank you all for the information in this great forum. Purchased this unit a couple weeks ago from an auction. Did lots of reading here, downloaded the TMs, have been reading them as well.
Went last week and picked up this generator and was pretty happy with it. Low hours 208 on the meter and looking it over appears to be actual hours. Got it home and started cleaning out the fuel system. Wow, lots of yuck all through it. I did not open the IP or do anything past it. Broke the fuel line at the IP due to trying to take it apart with the wrong nut. Found a new line and ordered it. Finished cleaning, new filters, and put all back together minus the fuel line I broke. While waiting on that figured would start checking other functions. All 3 fuel pumps kicked in, fuel stared flowing to the check valve. Happy guy at that point. Hit the start switch to see if the fuel shutoff solenoid worked. Engine turned over was puffing a little white smoke which gave me hope she would fire when I get fuel line in. Fuel solenoid did not work, but I could move it by had easily. Tested it and would not work, was getting 24 volts. So today fuel line comes in, get it put on try starting again, still no fuel solenoid. Took the solenoid out, jumped it to 24v and it actuated, did that a couple times, put it back in and walla all is good. Unit fired right up and purred.
Tested output voltage and it makes power, while testing checked batt voltage and it was overcharging. Shut it down. Later I hooked up to the outputs and ran a 5000 watt 240v heater and while running it was checking batt volts again and it was charging right at 27 volts so seems that is all good.
So far a very happy guy with my action purchase.
Few issues to work through.
1 fuel tank has a pin hole in the bottom have to fix
2 shutters/cooling is sticking, working some pb blaster and stuff on those points to get it free
3 hz meter reading way high pegged out, fluke meter running 60hz.
Any suggestions on the fuel tank repair and the meter issues? I see the transducer is a common issue with the meter. I wouldn't be against swaping all gauges to digital if someone could point me in a direction of locating good set that would fit.
Thanks again for all the info reading through the posts.
Went last week and picked up this generator and was pretty happy with it. Low hours 208 on the meter and looking it over appears to be actual hours. Got it home and started cleaning out the fuel system. Wow, lots of yuck all through it. I did not open the IP or do anything past it. Broke the fuel line at the IP due to trying to take it apart with the wrong nut. Found a new line and ordered it. Finished cleaning, new filters, and put all back together minus the fuel line I broke. While waiting on that figured would start checking other functions. All 3 fuel pumps kicked in, fuel stared flowing to the check valve. Happy guy at that point. Hit the start switch to see if the fuel shutoff solenoid worked. Engine turned over was puffing a little white smoke which gave me hope she would fire when I get fuel line in. Fuel solenoid did not work, but I could move it by had easily. Tested it and would not work, was getting 24 volts. So today fuel line comes in, get it put on try starting again, still no fuel solenoid. Took the solenoid out, jumped it to 24v and it actuated, did that a couple times, put it back in and walla all is good. Unit fired right up and purred.
Tested output voltage and it makes power, while testing checked batt voltage and it was overcharging. Shut it down. Later I hooked up to the outputs and ran a 5000 watt 240v heater and while running it was checking batt volts again and it was charging right at 27 volts so seems that is all good.
So far a very happy guy with my action purchase.
Few issues to work through.
1 fuel tank has a pin hole in the bottom have to fix
2 shutters/cooling is sticking, working some pb blaster and stuff on those points to get it free
3 hz meter reading way high pegged out, fluke meter running 60hz.
Any suggestions on the fuel tank repair and the meter issues? I see the transducer is a common issue with the meter. I wouldn't be against swaping all gauges to digital if someone could point me in a direction of locating good set that would fit.
Thanks again for all the info reading through the posts.