Runs fine. Quit producing power. Moved start switch to flash field, did not help. What could it be?
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
No power at convenience outlets.Chainbreaker wrote: Any power at "Convenience Outlets" on Gen set? This is an important question.
Okay thanksProbably should ohm out CVT-1 per the TM to see if you have an issue there.
I have a TM for it. I checked CT1 (not CVT) and 1C to 2C reads 0.2 ohms instead of 0.5. Do I need to unhook all the wires to read it, or only the terminals I’m testing?Are you good with the TM's, or need a little help?
All help is appreciated!I have a TM for it. I checked CT1 (not CVT) and 1C to 2C reads 0.2 ohms instead of 0.5. Do I need to unhook all the wires to read it, or only the terminals I’m testing?
On CT1 1A-2A 0.55Thanks! I will check it out.