Brief history! I bought the machine used. Very cheap! Guy had it for years just sitting in a trailer. Supposedly ran when he put it there. I was able to get the fuel system cleaned.
The phase selector was stuck in the straight up position but I was able to get it freed by oil and tapping.
Then with the help of @Ray @jamawieb @Chainbreaker and others I was guided into finding that the plunger was split in half. Now that all those issue have been fixed I can move on.
I ran the unit today perfectly for a few hours. I then decided to test the voltage so I could prepare to put a load on the system. My voltage regulator by the blower wheel I plan to replace.
Front convenience receptacle works fine.
I was able to measure lugs but I’m only producing 120v from L3 to L0. That’s the only voltage across any combination of the lugs. The switch is set far right 120/220v. I measured the lugs with two different known good meters in every combination I could.
However the panel meter reads almost correct but if I switch the ammeter/voltmeter to the
1
L3-L1
L3
Setting the volt gauges reads around 208
Seems it’s making the power?
And in the
L3
L3-L0
1
Position it reads 120v
Seems correct to my best understanding!!
voltage adjust knob works I can turn the voltage up and down.
I did notice that on my panel door that covers the lugs someone wrote
X over lug 1
L1 over L2
L2 over L3
N over L0
Not sure if maybe someone wired it to only do 120v??
See pic below. Maybe I’m missing something
If anyone has any suggestions or where to begin I would greatly appreciate it. I would
Love to get it figured out tomorrow and begin load testing so it’s ready to power my house. Thanks again!!
The phase selector was stuck in the straight up position but I was able to get it freed by oil and tapping.
Then with the help of @Ray @jamawieb @Chainbreaker and others I was guided into finding that the plunger was split in half. Now that all those issue have been fixed I can move on.
I ran the unit today perfectly for a few hours. I then decided to test the voltage so I could prepare to put a load on the system. My voltage regulator by the blower wheel I plan to replace.
Front convenience receptacle works fine.
I was able to measure lugs but I’m only producing 120v from L3 to L0. That’s the only voltage across any combination of the lugs. The switch is set far right 120/220v. I measured the lugs with two different known good meters in every combination I could.
However the panel meter reads almost correct but if I switch the ammeter/voltmeter to the
1
L3-L1
L3
Setting the volt gauges reads around 208
Seems it’s making the power?
And in the
L3
L3-L0
1
Position it reads 120v
Seems correct to my best understanding!!
voltage adjust knob works I can turn the voltage up and down.
I did notice that on my panel door that covers the lugs someone wrote
X over lug 1
L1 over L2
L2 over L3
N over L0
Not sure if maybe someone wired it to only do 120v??
See pic below. Maybe I’m missing something
If anyone has any suggestions or where to begin I would greatly appreciate it. I would
Love to get it figured out tomorrow and begin load testing so it’s ready to power my house. Thanks again!!