Mep 002a voltage

Triple Jim

Well-known member
1,375
287
83
Location
North Carolina
Read my last post please. You're on the wrong transformer. You're measuring "1C" and "2C" of CT1 when you need to be on "C1" and "C2" of CVT1.

Note that the diagram label "front" is away from you when you're looking in the enclosure. C1, X2, and C1 are nearest CT1.
 
Last edited:

RJM27

Active member
359
30
28
Location
Burdett NY
I just went out to my MEP-003A and looked. You're on CT1. CVT1 is the one that's away from where you're sitting when you look at the pair. CT1 should have "CT1" molded into the housing facing you. That's the wrong one.

Put those wires back on and find C1 and C2 on CVT1. I found a diagram someone drew that shows the terminals. Locate screw terminals C1 and C2 and verify you have the correct terminals by finding the markings near them, molded into the plastic. Remove the wire from one of them and measure the resistance between those two screw terminals on the transformer. You may have to remove the wires from both of the terminals so you can see the "C1" and "C2" molded into the plastic, therefore indicating you have the correct ones.

View attachment 799448
Alleluia!!!!
 

Attachments

Triple Jim

Well-known member
1,375
287
83
Location
North Carolina
OK, so the control winding of CVT1 looks good. Everything is pointing to the regulator board. You did say it's an intermittent problem, which means you might have just caught CVT1 when it was behaving. Therefore it's not a 100% certainty unless you swap it with the one in your other generator, but that's what it looks like.
 

RJM27

Active member
359
30
28
Location
Burdett NY
OK, so the control winding of CVT1 looks good. Everything is pointing to the regulator board. You did say it's an intermittent problem, which means you might have just caught CVT1 when it was behaving. Therefore it's not a 100% certainty unless you swap it with the one in your other generator, but that's what it looks like.
1st off THANKS!! It is no longer intermittent producing 156-+ & 300 + consistent, not able to swap parts, suggestions to what I should replace 1st & supplier very helpful
 

jamawieb

Well-known member
1,437
556
113
Location
Ripley/TN
Buy Triple Jim's board, best money I every spent. I've purchased a couple over the years for different units with VR problems. So if anyone needs an old board, that is not functioning, I'll let them go at a good price. ;)
 

RJM27

Active member
359
30
28
Location
Burdett NY
Many thanks to all, look forward to getting my security blanket back up & running!!! To all be safe & well!