Hello All,
Brand new to the forum. Last month I got an MEP 003A off ebay that was guaranteed to work. It didn't. The cost to return the unit od prohibitive. So it is no my problem.
I running down the diagnostic found on page 2-9 of TM5-6115-585-34 while praying that this is not an open winding. I installed a new voltage regulator today, but it did not fix the problem. When running on 1-phase / 220V, I get 562mV between L1 and L3 and 263mV from each to ground. I get the same 256mV on the convenience receptacles.
Using the procedure in paragraph 8.2 of the same TM, I checked two of the exciter diodes (the ones that I can get to). Resistance is 1.3M-ohm and 1.2M-ohm respectively. However both diodes tested open when I reversed the leads. I found two stores that listed the Onan 358-0037 and 358-0024 respectively, and ordered the diodes. However, both stores are reporting that these part numbers are on back-order status (not a good sign). If someone has a cross-referenced part number for these, along with 1N4246, I would appreciate it.
For me the next step is to check generator rotor flashing circuit. In particular, the bridge rectifier (diodes 1N4246). If anyone is willing to work with me on a solution, I am grateful.
Brand new to the forum. Last month I got an MEP 003A off ebay that was guaranteed to work. It didn't. The cost to return the unit od prohibitive. So it is no my problem.
I running down the diagnostic found on page 2-9 of TM5-6115-585-34 while praying that this is not an open winding. I installed a new voltage regulator today, but it did not fix the problem. When running on 1-phase / 220V, I get 562mV between L1 and L3 and 263mV from each to ground. I get the same 256mV on the convenience receptacles.
Using the procedure in paragraph 8.2 of the same TM, I checked two of the exciter diodes (the ones that I can get to). Resistance is 1.3M-ohm and 1.2M-ohm respectively. However both diodes tested open when I reversed the leads. I found two stores that listed the Onan 358-0037 and 358-0024 respectively, and ordered the diodes. However, both stores are reporting that these part numbers are on back-order status (not a good sign). If someone has a cross-referenced part number for these, along with 1N4246, I would appreciate it.
For me the next step is to check generator rotor flashing circuit. In particular, the bridge rectifier (diodes 1N4246). If anyone is willing to work with me on a solution, I am grateful.
Service | NPN | Description | Mfg. / Part Nbr. | TM Ref. | Figure / Nbr. | Qty | Tot Qty |
Bridge Rectifier | 5961-00-914-9740 | Semiconductor Device, Diode | JAN1N4246 | TM5-6115-585-24P | 15 | 6 | 15 |
Voltage Reg. | 5961-00-914-9740 5961-00-900-0064 | Semiconductor device, Diode | 1N4246 JAN1N4246 | TM5-6115-585-24P | | 7 | 13 |
Generator Rotor | 5961-01-050-7048 | Semiconductor Device, Diode | 72-5273-2 ST Semicon S6248R Onan 358-0037 | TM5-6115-585-24P | 26 / 27 | 3 | 3 |
Generator Rotor | 5961-01-054-4151 | Semiconductor Device, Diode | 72-5273-1 ST Semicon S6248 Onan 358-0024 | TM5-6115-585-24P | 26 / 28 | 3 | 3 |