Speddmon, I was following your input on the MEP-003a hookup and have a question about the 005a.
http://www.steelsoldiers.com/auxillary-equipment/40290-mep-003a-hook-up-question-4.html
Looking at the wiring diagram for the 005a, the L0 terminal is grounded to the chassis. Am I seeing that right?
If I am hooking up the unit as a non-SDS and do not have the grounded condutor switched, should I disconnect the neutral from the chassis ground? Happen to know where that connection is located.
Thanks,
Warthog
P.S. I fixed the issue with the field exciter. The Voltage regulator box was barely attached with one bolt and the surface very rusty. I checked all the componates and they where good. After a good cleaning and more bolts it worked fine. I will update my other post.
http://www.steelsoldiers.com/auxillary-equipment/40290-mep-003a-hook-up-question-4.html
Looking at the wiring diagram for the 005a, the L0 terminal is grounded to the chassis. Am I seeing that right?
If I am hooking up the unit as a non-SDS and do not have the grounded condutor switched, should I disconnect the neutral from the chassis ground? Happen to know where that connection is located.
Thanks,
Warthog
P.S. I fixed the issue with the field exciter. The Voltage regulator box was barely attached with one bolt and the surface very rusty. I checked all the componates and they where good. After a good cleaning and more bolts it worked fine. I will update my other post.