I just acquired an MEP-016E with only 8.3 hours since a complete rebuild. Everything in this one is pretty much as clean as when it shipped from Ft. Hood TX.
Runs like a champ, but no output on the 120 volt plug on front. I used the voltmeter switch on the front to look at the voltages. 1-0 is about 100v, 2-0 is about 100v, 3-0 is zero volts.
I started tracing out the wiring from the panel mounted schematic as well as a downloaded schematic MEP-016b versions from the web.
Here's the problem I found:
All of the schematics I found show that the generator windings should be:
T1-T4
T2-T5
T3-T6
What I measured (with the windings disconnected from the terminal strip):
T1-T5 0.6 Ohm
T2-T6 0.6 Ohm
T3-T4 0.6 Ohm
All wiring looks new, and there are no shorts to ground in any of the windings.
I can't imagine that they would have changed the winding connections for the "E" version.
I'm wondering if the generator windings are simply labeled wrong? Either by receiving a new generator with them wrong, getting distracted, or maybe seeing how good the new guy is at troubleshooting?
Thanks guys, this is my first post, and I promise I'll follow up with what I find. It's better to share the knowledge than to simply drop out of sight after it's solved.
Flatdog555
Runs like a champ, but no output on the 120 volt plug on front. I used the voltmeter switch on the front to look at the voltages. 1-0 is about 100v, 2-0 is about 100v, 3-0 is zero volts.
I started tracing out the wiring from the panel mounted schematic as well as a downloaded schematic MEP-016b versions from the web.
Here's the problem I found:
All of the schematics I found show that the generator windings should be:
T1-T4
T2-T5
T3-T6
What I measured (with the windings disconnected from the terminal strip):
T1-T5 0.6 Ohm
T2-T6 0.6 Ohm
T3-T4 0.6 Ohm
All wiring looks new, and there are no shorts to ground in any of the windings.
I can't imagine that they would have changed the winding connections for the "E" version.
I'm wondering if the generator windings are simply labeled wrong? Either by receiving a new generator with them wrong, getting distracted, or maybe seeing how good the new guy is at troubleshooting?
Thanks guys, this is my first post, and I promise I'll follow up with what I find. It's better to share the knowledge than to simply drop out of sight after it's solved.
Flatdog555