ThanksOnly one ground rod in the system.
The ground wires can also carry current, and there can be issues if there is an imbalance in the system due to multiple ground rods.
It used to be code to ground standby generators at the generator, but current code is that the grounding goes through the house system, and grounds at the gen are not allowed.
Code in my area calls for additional grounds at detached buildings (which are tied into the panel and structure), but one and only one point of bonding (service entrance, before first use).Only one ground rod in the system.
The ground wires can also carry current, and there can be issues if there is an imbalance in the system due to multiple ground rods.
It used to be code to ground standby generators at the generator, but current code is that the grounding goes through the house system, and grounds at the gen are not allowed.
This is accurate per the NEC. You can drive as many ground rods as you'd like, but it can only be bonded to the neutral at the first means of disconnect. Our code requires ground rods at any outbuildings as well. Its also smart to have one for the gen set too.Code in my area calls for additional grounds at detached buildings (which are tied into the panel and structure), but one and only one point of bonding (service entrance, before first use).
I sorted through this topic a while back in this post:
Outlet plug for my 803
Got my outlet plug and cover all sealed up and painted. -- Carlwww.steelsoldiers.com
This doesn't apply to the OP's situation, however for anyone coming along and using this thread's info to gnd their generator there is a caution though. I am of the understanding there is a distance restriction on how close a gnd rod can be to the main house panel's gnd rod. I recall reading somewhere you do not want to drive an additional gnd rod at generator closer than ~25' of the main panel's gnd rod when generator uses a 4 conductor hookup utilizing electrical panel gnd. The issue is potential for developing ground loop currents if gnd rods are too close to one another.This is accurate per the NEC. You can drive as many ground rods as you'd like, but it can only be bonded to the neutral at the first means of disconnect. Our code requires ground rods at any outbuildings as well. Its also smart to have one for the gen set too.
use the services of a "Licensed Electrician" to insure your hook-up is in compliance with your local electrical codes.
Having it checked every other week seems excessive, but it really depends on what the standby generator is classified as..
Thinking about our neighbor at the print shop...
They have a dispatch center here in the mechanical building. Every other week, promptly at 0800, their propane powered generator kicks off and runs at speed for a half hour. Unattended. Nobody walks out there and looks at it or opens the fence or anything else. It just fires up and runs. Same time on the alternating week, one of the mechanics (same one every time) comes out and checks the engine oil and radiator fluid level.
The switch gear is automated and there is a battery bank between the equipment and power.
It seems like a heck of a nice way to have power and know that they have a functional backup power source.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!