I'm splitting this topic from the THIS thread. I think it's worth covering separately the black smoke from my genset while load testing it. HERE is a video of the test.
I already received great feedback:
I assume adjusting the IP would take rotating them to allow less or more fuel. If that's the case, clockwise increases the flow, right?
I already received great feedback:
Usually once you get them cleared out you should have virtually no visible smoke until pretty close to or sometimes even above 100%.
You will vary slightly from 1 machine to the next, but in general you should get pretty close to 100% load with not much smoke. If you see smoke coming on way too early you either still have carbon buildup or 1 of the metering pumps may be adjusted incorrectly.
The best way to identify a mis-adjusted pump is to use an IR thermometer to compare EGT between cylinders or best way is to remove the exhaust manifold and you will see the offending cylinder right away. Although removing the manifold at this point may be a bit of work in your instance.
I don't mind removing the hood and the cover, I just used a few bolts to keep it in place. I checked the temperature between cylinders on the outside of the exhaust ports and they are not the same, they are close but not in the same range. On top of it, the reading changes by moving the IR dot by just a 16th of an inch. What would be the most accurate way of checking this? What should I look for after removing the exhaust manifold?I looked at the video, It's a bit hard to tell but the smoke looks black.
Since you said 1 cylinder has some tar coming out of it my guess is either 1 injection pump is not metering properly or an injector isn't firing right.
I assume adjusting the IP would take rotating them to allow less or more fuel. If that's the case, clockwise increases the flow, right?