So pretty much wrapping up my process of getting the 803a going. Had it running on the load bank the other night and it will handle no problem 13500 watts resistive load. Throws the percent load meter to a little over 100%. My load bank is simply 6 4500 water heater elements I built it to load up my 005a wish I had smaller steps now between elements. Any way three of them were switched on and just to see what she would do I threw on the switch for the fourth one. I believe that is around 16000 watts or so, way over what the unit is rated for. Well as you can see in the first video the one filmed at night the motor just starts to bog down pretty much just a givn er but just dosent have the poop to do it. Well I did not leave it in dropped off one 4500 element and it sort of recovers but not really till I dump more load off.
So the next day I tried this one more time with the forklift charger running so a little less than 16000 watts 3 elements and the forklift charger comes out to more like 14k somethin. Any way I found the generator will do it if I throttle it up to full throttle and then drop it in however you can see the exhaust it is really workin hard to do it. As soon as I throttle down a little to bring it into 60hz the motor just starts to bog so I drop an element again to lighten the load.
Couple questions bout all this why is the overload not kickin it and opening up the contactor? I performed the test procedure as it is outlined in the TM for the over current/ short circuit relay seemed to test okay on the first test however the #2 terminal and #3 terminal on the overload relay just threw the short circuit light as soon as I closed the contator. Perharps this part is bad? Not to worried about it never going to be pushing this thing this hard at the house was just curious at what point they usually open up. From the reading on here looks like around 13000 watts or so.
The other thing is if the motor can keep up with the load put on it when you manually throttle it why is the governor not asking for full throttle and allowing the motor to keep up instead of bogging down?
Attached are the first and second videos so you can see what I am talking about.
https://youtu.be/i80uZSanc7o
https://youtu.be/cR1DhfWZPdE
Lee
So the next day I tried this one more time with the forklift charger running so a little less than 16000 watts 3 elements and the forklift charger comes out to more like 14k somethin. Any way I found the generator will do it if I throttle it up to full throttle and then drop it in however you can see the exhaust it is really workin hard to do it. As soon as I throttle down a little to bring it into 60hz the motor just starts to bog so I drop an element again to lighten the load.
Couple questions bout all this why is the overload not kickin it and opening up the contactor? I performed the test procedure as it is outlined in the TM for the over current/ short circuit relay seemed to test okay on the first test however the #2 terminal and #3 terminal on the overload relay just threw the short circuit light as soon as I closed the contator. Perharps this part is bad? Not to worried about it never going to be pushing this thing this hard at the house was just curious at what point they usually open up. From the reading on here looks like around 13000 watts or so.
The other thing is if the motor can keep up with the load put on it when you manually throttle it why is the governor not asking for full throttle and allowing the motor to keep up instead of bogging down?
Attached are the first and second videos so you can see what I am talking about.
https://youtu.be/i80uZSanc7o
https://youtu.be/cR1DhfWZPdE
Lee