Just found this forum. What a treasure trove of info!
My brother picked a practically new MEP-805B and used it for over a year. Then one day the engine just shut down. He thought it was out of fuel - nope. He's the mechanical guy; I'm supposed to be the electrical guy. We finally pinned it down to the fuel actuator valve isn't getting a signal. At first we thought it was just an on/off fuel solenoid, but later realized it's the business end of the governor. I can power the actuator separately and control engine speed. But can't get the automatic speed regulator to work. The magnetic rpm pickup must be working because the generator frequency is displayed on the CIM screen. We have the whole TM.
One thing I can't find is the Governor Control Power Relay. It's shown on the block diagram on page 1-20, and is referenced in paragraph 1.16.3.3 . It says that it is connected to the Fault System, but I can't find it on the wiring diagrams or schematic. Any help finding this would be most welcome.
I'm about to install a variable power supply with a front panel pot that will let us set engine speed. This will probably do as long as the load doesn't change too much, but Automatic would be lots better. Read many of the 805B posts, but nothing seems close enough.
TIA Don
My brother picked a practically new MEP-805B and used it for over a year. Then one day the engine just shut down. He thought it was out of fuel - nope. He's the mechanical guy; I'm supposed to be the electrical guy. We finally pinned it down to the fuel actuator valve isn't getting a signal. At first we thought it was just an on/off fuel solenoid, but later realized it's the business end of the governor. I can power the actuator separately and control engine speed. But can't get the automatic speed regulator to work. The magnetic rpm pickup must be working because the generator frequency is displayed on the CIM screen. We have the whole TM.
One thing I can't find is the Governor Control Power Relay. It's shown on the block diagram on page 1-20, and is referenced in paragraph 1.16.3.3 . It says that it is connected to the Fault System, but I can't find it on the wiring diagrams or schematic. Any help finding this would be most welcome.
I'm about to install a variable power supply with a front panel pot that will let us set engine speed. This will probably do as long as the load doesn't change too much, but Automatic would be lots better. Read many of the 805B posts, but nothing seems close enough.
TIA Don