MEP-831A 3kw generator, overload @ 2.4kw

remcauliffe

New member
4
3
3
Location
Fla
Greetings, looking for some trouble shooting assistance. My MEP-831A runs well but trips overload after running for less than a minute at loads above 2.4kw. I’ve removed and inspected the inverter assembly and didn’t see any evidence of leaking / damaged capacitors or overheating of components on the CCAs. Any suggestions on how to proceed with troubleshooting would be appreciated.


Sent from my iPhone using Tapatalk
 

kloppk

Well-known member
Steel Soldiers Supporter
2,205
3,762
113
Location
Pepperell, Massachusetts
What mode is the inverter set to? 120 or 120/240?
If 120/240 is your load balanced? L0 to L1 and L0 to L2? Is it a 240 volt load (L1 to L2) or two 120 volt loads L0 to L1 and L0 to L2)?
In 120/240 mode if either load is greater than 1,500 watts the Overload will occur.

Remember, the Inverter is actually comprised of two 1,500 wat inverters inside it. Both have Overload protection.
When in 120 mode the two inverters are synchronized and connected in parallel to provide 120 volts 3,000 watts.
When in 120/240 the two inverters are set 180 degrees out of phase and are connected in series to provide 240 volts.
 

remcauliffe

New member
4
3
3
Location
Fla
I’m running in 120V mode, off of L1 for this test. I installed a supplemental 120V 20A receptacle, which is fed from L1.


Sent from my iPhone using Tapatalk
 

remcauliffe

New member
4
3
3
Location
Fla
I was able to sustain 2.7kw for about 15 minutes with no issues so it appears that the jumper worked. So that would indicate that a relay isn’t latching? Any idea which relay I should check out? Interestingly, when I loaded up to 3kw, the governor started to intermittently close. Keep running but slamming shut and resuming about every 2 seconds. Any suggestions on that? Thanks guys!


Sent from my iPhone using Tapatalk
 

remcauliffe

New member
4
3
3
Location
Fla
I’ll go through the adjustment procedure and see what yields. I installed the digital governor controller a while back so I don’t think that would be the problem.


Sent from my iPhone using Tapatalk
 