MEP-831A Neutral Ground Bond

zapp

Member
30
32
18
Location
Ohio
Hi - I looked in the manual but didn't see reference to a removable neutral/ground bar like the 802A/803A's have if you want to hook up to a home with a disconnect. From what I read code requires only one place where neutral/ground is bonded and that is generally in the existing panel. The 803A has a simple bar to remove the bonding. Anybody added a switch or changed their's?
 

zapp

Member
30
32
18
Location
Ohio
Thanks! I'll unhook and check continuity between N-G to confirm. I was thinking of putting a switch in place to be able to toggle when I need it bonded (stand alone) and then when I don't (connected to home). Assuming just a SPST switch rated at 240V should work.?
 