- 5,368
- 3,379
- 113
- Location
- Lexington, South Carolina
Lots of people have talked about how strong these generators are under normal circumstances, and several of us have commented about the Army testing method to determine the limits of power output. Well, I found a picture, courtesy of GL that explains it much better, and more definitively than any of what we might say. It is a dataplate attached to a MEP 30 KW generator that can be configured to run 110/208 3 phase or 240/416 3 phase
In case you cannot read it:
__KW_______Elevation________Temp
_25/30_______5000 ft_________107 F
_25/30_______6000 ft_________103 F
_22.5/27_____8000 ft__________95 F
In case you cannot read it:
__KW_______Elevation________Temp
_25/30_______5000 ft_________107 F
_25/30_______6000 ft_________103 F
_22.5/27_____8000 ft__________95 F
Attachments
-
38.7 KB Views: 20