Mep002/3 Question

captnkirk

New member
10
0
0
Location
northeast oh
Hello
I am not reading any voltage on L1, am getting 120v on L3.
(trying to get 240 single phase)
also i have another unit that i am getting 62 volts on L1 and L3.
Thanks
Kirk
 

Isaac-1

Well-known member
1,970
50
48
Location
SW, Louisiana
The low voltage unit is probably a problem with a bad diode in the rectifier bridge (easy fix), there should be testing procedures in the TM, or may be the voltage regulator, or less likely a problem in the windings.

Ike
 

Speddmon

Blind squirrel rehabiltator
Super Moderator
Steel Soldiers Supporter
4,640
28
38
Location
Cambridge, Ohio
Change position of the main reconnection switch several times, make sure it "snaps" into each position. And if that doesn't work out, open up the box under the connection lugs and make sure you have the proper voltages on both sides of the main breaker (CAREFULLY). That has been an issue for people in the past.
 