Hooked the mep003a up to the house for the first time to get ready for Sandy.
Moved the Circuit switch to 1 phase 220 volts.
Things went well as I snapped on light breakers, the electric hot water tank, the freezer, and as I added more light breakers (lights were off for these breakers) all lights and I guess the hot water tank, and freezer went dead. Checked the AC breaker out at the gen. it was still in on position. Checked gen. panel volt meter it read 220 volts L3 to L1 and 120 volts L1 to L0. When I put a volt meter across L1 to L3 power out terminal it read about 150 volts; from L3 to L0 120 volts and from L1 to L0 about 50 volts.
I plugged in a 500 watt light to the 120V AC receptacle in the front of the panel, it worked fine.
Anyone have this problem. Any suggestions how to further check or fix it.
Charlie
mep003a
m116A2
Moved the Circuit switch to 1 phase 220 volts.
Things went well as I snapped on light breakers, the electric hot water tank, the freezer, and as I added more light breakers (lights were off for these breakers) all lights and I guess the hot water tank, and freezer went dead. Checked the AC breaker out at the gen. it was still in on position. Checked gen. panel volt meter it read 220 volts L3 to L1 and 120 volts L1 to L0. When I put a volt meter across L1 to L3 power out terminal it read about 150 volts; from L3 to L0 120 volts and from L1 to L0 about 50 volts.
I plugged in a 500 watt light to the 120V AC receptacle in the front of the panel, it worked fine.
Anyone have this problem. Any suggestions how to further check or fix it.
Charlie