MEP005 will not flash

s011883

Member
39
2
6
Location
Hartford MI
Hello. I have a 30 kw generator that will not flash by itself. If you take a 9 volt battery and manually flash the generator on the side, It will start producing power and continue until you shut it off. I've sent the speed switch and exciter box to Delk's to check it out. He put them on a running unit and said there is nothing wrong with them. How should I proceed? The military must have had the same problem, because the speed switch is brand new. I also checked all the wiring and everything checked out ok.
 

Warthog

Moderator
Super Moderator
Steel Soldiers Supporter
13,774
232
63
Location
OKC, OK
Pull the excited box out and take off the cover. Tighten each and every screw or bolt. I had a unit that had the same problem. There where a couple of screws that where loose and would make intermitant contact.
 

s011883

Member
39
2
6
Location
Hartford MI
I have done it both ways, but just for a split second, and then it will take off. I have also taken the exciter apart, checked every connection, and the bolts. ImageUploadedByTapatalk1395285331.166610.jpg
 