MEP 803a does not crank. Power available at CB-1. Main switch voltage across #6 is 25vdc in stop and 0 at prime/run. The relays and fuel pump do not click. Generator started and ran fine 2 days ago with a normal shutdown after a 2 hour load test. No warning/alarm lights. Fuel level is high. Oil level is still showing on dipstick. Visible fuses are good. Any help? I have a hurricane heading this way next week. The deadcrank worked intermittently but I pulled the switch and when it is on normal mode the circuit is closed between 2 and 3 I have voltage. When I jump terminal 1 and 2 on the deadcrank I get no response. I have good voltage on #2.