- 114
- 208
- 43
- Location
- Fredericton, New Brunswick, Canada
Recently got the 803 running.
Put approx 18hrs run time in the last week performing various load test. Have access to various 5A, 10A , 20 and 23A 240v load. I was able to bring the load to 60A - 115% - Once and set ran fine. Problem is I can't do it consistently. If I try to step up the load by more than 10A at the time the set bog down to very low idle , If i flip the breaker off quickly it goes back to speed immediately. Always take load fine from 0 to 20A load , will bog down if I load to quickly after that ( regardless if I'm at 25,35,45A...) . Never tripped the overload fault.
In the last 4 days I read every post I could find and tested every suggestions. Ran set at every load above 50% for an hour or 2. At least 4 hrs between 80% and 100% load. No obstruction to air intake. Changed again both fuel filters. Sea foam in filter when I changed. And sea foam added to tank. Hertz variation between 0 load and 115% load is less than 2.3 hertz . Less that 1.5°F between any cylinder at any load
No signs of wet stacking. Temp steady at 190° at any load. Oil pressure steady at 35-40 psi. When set bog down on load no black/white smoke out of exhaust. Re-read TM. It's really feel like the governor is not responding quickly enough when load is added ( I saw you tube video where they go from 0 to 133% load by flicking K1 and set doesn't bog down) droop ? Voltage regulator? Thanks
Put approx 18hrs run time in the last week performing various load test. Have access to various 5A, 10A , 20 and 23A 240v load. I was able to bring the load to 60A - 115% - Once and set ran fine. Problem is I can't do it consistently. If I try to step up the load by more than 10A at the time the set bog down to very low idle , If i flip the breaker off quickly it goes back to speed immediately. Always take load fine from 0 to 20A load , will bog down if I load to quickly after that ( regardless if I'm at 25,35,45A...) . Never tripped the overload fault.
In the last 4 days I read every post I could find and tested every suggestions. Ran set at every load above 50% for an hour or 2. At least 4 hrs between 80% and 100% load. No obstruction to air intake. Changed again both fuel filters. Sea foam in filter when I changed. And sea foam added to tank. Hertz variation between 0 load and 115% load is less than 2.3 hertz . Less that 1.5°F between any cylinder at any load
No signs of wet stacking. Temp steady at 190° at any load. Oil pressure steady at 35-40 psi. When set bog down on load no black/white smoke out of exhaust. Re-read TM. It's really feel like the governor is not responding quickly enough when load is added ( I saw you tube video where they go from 0 to 133% load by flicking K1 and set doesn't bog down) droop ? Voltage regulator? Thanks
Attachments
-
51.6 KB Views: 13