JRM
Member
- 166
- 12
- 18
- Location
- Brightwood, Oregon
I own a 803A that's awesome, but I Need EXPERT advice on a non MEP as my father's death forced a move to his home that has a backup genset, a Honda EB12D that's pretty good as well. I found it on craigslist, and it's been solid as a rock.... until this weekend during the worst storm iv seen in my 45 years here. Genny was purring along great then all a sudden shutdown like the key was turned off. I think it's the fuel shutoff solenoid but not 100% sure, here is what I checked.
* Unit starts up just fine, then the second i let off the key and it returns from start to the run pos it shuts down.
* Oil pressure and temperature sensors checked ok. Unit does not run with them disconnected.
* 12V system is ok, plenty of power to hold open the solenoid
* I still here a distinct click of the solenoid when i turn on the key, just as it always had- can it still be the problem?
* Fuel system is not the problem. Its clean as a whistle and it shut down instantly.
Im pretty confident on the solenoid as being a dodge 12V owner, it happends exactly the same?
Other ideas welcome!
Oh, and moveing the MEP to this house IS in the plans..... brushless and 1800RPM way better
* Unit starts up just fine, then the second i let off the key and it returns from start to the run pos it shuts down.
* Oil pressure and temperature sensors checked ok. Unit does not run with them disconnected.
* 12V system is ok, plenty of power to hold open the solenoid
* I still here a distinct click of the solenoid when i turn on the key, just as it always had- can it still be the problem?
* Fuel system is not the problem. Its clean as a whistle and it shut down instantly.
Im pretty confident on the solenoid as being a dodge 12V owner, it happends exactly the same?
Other ideas welcome!
Oh, and moveing the MEP to this house IS in the plans..... brushless and 1800RPM way better