USAMilRet
- 15
- 18
- Tampa, Florida
Yea....getting my 803 in a couple of days. Sitting on a pallet in Tampa. Was doing some calculations and can see that 10kw is not a safe output figure. Some of these can go to 14kw and run all day long. This begs the question that at 14kw 240VAC means a feed output of 58Amps. Much more than the rated output of 51 Amps given as the standard output at .8 pf. While at 12.5kw @240VAC is 52A and a 220V is 56.8A
When tying into the house, shouldn't you use a 60A dual pole circuit breaker for power into the panel after interlock placement?
Why wouldn't you want to use the full output if the genset runs with no issues?