mep004
Guyfang
24,064
Burgkunstadt, Germany
Have you downloaded the TM's?
Your problem is probably in the S9-1 circuit or the Static Exciter. Initial excitation is done by the start switch. After the main gen lights off, the Static Exciter/volt Regulator takes over. You are getting initial excitation.
jamawieb
556
Ripley/TN
Pull the exciter box that is above the starter and take the cover off. I beat it's the T2 transformer is burned up. 1st option is to try and replace the transformer but more things will go bad or convert over to a modern Voltage regulator. Several threads about it, most recent being one of mine on a 005a. The 004a and 005 use the same set-up for almost everything. I really like the Marathon AVR I used in a 3 phase application.
catienla
anawalt,wv
Thanks guys. I have very little experience with this gen set, it has been fine since 2011 when I purchased it. I'll check the regulator. One more question, does the dc power for this come from the alternator on the engine or from the generator?
jamawieb
556
Ripley/TN
DC comes from the alternator on the motor.
Guyfang
24,064
The power comes from the DC system. The gen set runs just fine without an alternator. Battery power, or even jumped off from another gen set. If the set starts, you have the initial excitation voltage at hand.