• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

003A running fine but amp load meter failed

reybo

New member
59
0
0
Location
Charlottesville, VA
While using the gen last month, I switched on the house AC. The load meter was close to zero at the time, as we weren't running anything that drew amperage. It overloaded the gen and kicked off the breaker. I turned off the AC, reset the breaker, and all was fine except that the current meter was dead.

It appears there are two transformers in the circuit as well as the meter which may have blown. I learned this morning that the voltage to the meter should be 240 so I'll check that.

But in addition to clearing the meter problem I need to know why it happened. It's a medium size whole house AC which my calculations 4 years ago showed were within the capabilities of an 003. Are modifications needed? Does the distributor box need a special control for amperage-sucking AC?

The meter is a 6625-01-038-6839 (35.7001) On line I found this picture of a replacement to mine made by A&M Instruments as 366-043. May need one.

Regards to old friends here who 4 years ago helped me choose a gen and set it up. Wife and I need med machines whether the grid is up or down, and Mr. Libby makes it happen.
 

Attachments

jamawieb

Well-known member
1,435
557
113
Location
Ripley/TN
Is your voltage gauge working? Are you reading 120 at each leg? It may just be the gauge, they are known to fail. I would take some electrical cleaner and spray the reconnection switch while turning it from 240 single phase to 208 3 phase several dozen times. Sometimes the connections get dirty that will cause your problem.
 

reybo

New member
59
0
0
Location
Charlottesville, VA
Is your voltage gauge working? Are you reading 120 at each leg? It may just be the gauge, they are known to fail. I would take some electrical cleaner and spray the reconnection switch while turning it from 240 single phase to 208 3 phase several dozen times. Sometimes the connections get dirty that will cause your problem.
Interesting consideration. Thanks.
 

69birdman

Active member
201
139
43
Location
Summerfield, Fla.
I have an extra phasotron gauge I purchased to replace one on my 803a as I thought mine quit working. After spraying electrical cleaner and working the switches, it began to work again.
 

69birdman

Active member
201
139
43
Location
Summerfield, Fla.
All I could find locally @ auto parts store was a CRC brand marine grade, electronics connection cleaner. I've heard "Dexoit" is best, but have to order online. :beer:20180802_103155.jpg20180806_145322_001.jpg
 
Last edited:

Ray70

Well-known member
Steel Soldiers Supporter
2,627
6,034
113
Location
West greenwich/RI
Hey Reybo, if all else fails, and the meter checks out ok, check the CVT down in the bottom of the AC re-connection box. The TM tells you how to test it by measuring the resistance between a series of terminals.
 

csheath

Active member
714
213
43
Location
FL
The load gauge was dead on my 803 when I got it.

I rigged a couple of these in it's place.
volt-amp.jpg

Can be had off ebay for around 10 bucks apiece but they come from across the pond so delivery time is slow.
 

155mm

Chief and Indian
Steel Soldiers Supporter
1,181
397
83
Location
Guymon, OK
The aftermarket gauge cluster that I use is about 20 on a mazon. I use 2 of them on our camper generator, and I use 3 of them on my load tester. About 20 a piece, I like having one on each leg to see how each one is loaded or not loaded. It does have a kwh counter that keeps running tabs on how many kwh is used.

Screenshot_31.png


its very simple to hook up, red wire goes to the leg you are testing, black to neutral, the circuit transformer (CT) goes over one of the wires that goes to the house, there is an arrow on the CT that points the direction of electricity flow

If you need, I can go mock up a setup from a 3k genny so you can 'see' how its done, just let me know.
 
Last edited:
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks