I'm studying the TM wiring diagram to answer a theory question that stems from my brother's commercial genset.
It is understood that the Neutral bond must be disconnected at the lugs (in most cases) to feed a structure service as NEC requires the Neutral to be bonded "at the first disconnect means"...unless there is a reason that NEC would necessitate the bond required at the set if there is no other "disconnect means". Ergo, if bonded at the panel, then must be un-bonded at the set.
It is understood that the Neutral needs to bonded at the lugs if the set is to be used in-field or off-grid as it would therefore be the "first disconnect means".
Now my query: if the set is un-bonded at the lugs and for whatever reason is left to run by itself, then is the convenience outlet in a "floating Neutral" configuration or is there a Neutral bond dedicated and isolated to the outlet? My theory concedes that if the bond is open at the terminal lugs then there would be no way internally to bond the outlet without bonding the lugs as a consequence since everything is intended to resort back to the source and the ground is intended to be an emergency return path should the Neutral fail.
Sent from my SM-G970U using Tapatalk
It is understood that the Neutral bond must be disconnected at the lugs (in most cases) to feed a structure service as NEC requires the Neutral to be bonded "at the first disconnect means"...unless there is a reason that NEC would necessitate the bond required at the set if there is no other "disconnect means". Ergo, if bonded at the panel, then must be un-bonded at the set.
It is understood that the Neutral needs to bonded at the lugs if the set is to be used in-field or off-grid as it would therefore be the "first disconnect means".
Now my query: if the set is un-bonded at the lugs and for whatever reason is left to run by itself, then is the convenience outlet in a "floating Neutral" configuration or is there a Neutral bond dedicated and isolated to the outlet? My theory concedes that if the bond is open at the terminal lugs then there would be no way internally to bond the outlet without bonding the lugs as a consequence since everything is intended to resort back to the source and the ground is intended to be an emergency return path should the Neutral fail.
Sent from my SM-G970U using Tapatalk