Can you maybe clarify or show how you have it wired up?
Are you running in 120/240 mode and putting individual 120V loads on L1 and L3?
If so, running an imbalanced load like that may be playing tricks on your ammeter.
Not sure what you mean by shop heater on 5000W pulling 80% on 1 leg??
You can't throw 5000W on 1 leg unless you are in 120V mode with all the load on L3.
Also, flipping S7 up while the set is already running may not activate it correctly, I believe you have to hold the fault test light button, start machine while holding it, flip up S7 then release the fault light button.