Picked up an 831a and a 802a. The 802a works great except the fuel gauge and pops CB1 if I leave it in Prime & AUX to long but that's another day of playing around.
So back to the 831a. It was freight shipped so no oil and fuel. Had to break open the high pressure line at the injector and jump 24VDC from the 802a to run the pump (no batteries in 831a) and I cranked it until I got fuel up there and now it will start no issues with the pull start. Yes I put oil in it also...
I preformed the Electronic Governor checks and tweaks and loaded the 831a to 3kw blows some black smoke but seems to be going away with more use. I also overloaded it and it opens the contactor like it should. Seems like everything is good to go except I can't get it to start with the starter. You can hear K2 clunk and that's it.
I did all the checks in the Field Level Troubleshooting in the TM
Checked K15 pins 1 and 9 (0 ohms)
Battle Switch Short pins 1 and 2 of S7 (0 ohms)
Check K2 X1 to X2 with diode removed (54.7 ohms)
Check Engine Solenoid K2-A2 to TP31 (1.6 ohms)
Checked TB3 TP30 to TP31 (25.93 VDC all the time)
CB1 works
E-Stop works
Diode CR1 good
And then I did some extra checks that were not in this TM:
K2-A1 to TP31 (25.90 VDC)
K2-A2 to TP31 when I try to start (0 VDC) Thinking K2 may be bad??? looked on flee bay could not find one?
Update: Found an K2 CONTINUOUS DUTY SWITCH RELAY SOLENOID 24 VOLT 4-TERMINAL HEAVY DUTY 1115615 Pretty sure it would work.
Note Gov Actuator does let go from the magnet target when I try to start with start switch
Question. Would be ok to jump 24 VDC to K2-A2 to see if the starter works? I could make a fused jumper???
There is alot of info in this site and you all seem to be very smart with these gensets. I have been doing alot and alot of reading in here before I decided to post.
So back to the 831a. It was freight shipped so no oil and fuel. Had to break open the high pressure line at the injector and jump 24VDC from the 802a to run the pump (no batteries in 831a) and I cranked it until I got fuel up there and now it will start no issues with the pull start. Yes I put oil in it also...
I preformed the Electronic Governor checks and tweaks and loaded the 831a to 3kw blows some black smoke but seems to be going away with more use. I also overloaded it and it opens the contactor like it should. Seems like everything is good to go except I can't get it to start with the starter. You can hear K2 clunk and that's it.
I did all the checks in the Field Level Troubleshooting in the TM
Checked K15 pins 1 and 9 (0 ohms)
Battle Switch Short pins 1 and 2 of S7 (0 ohms)
Check K2 X1 to X2 with diode removed (54.7 ohms)
Check Engine Solenoid K2-A2 to TP31 (1.6 ohms)
Checked TB3 TP30 to TP31 (25.93 VDC all the time)
CB1 works
E-Stop works
Diode CR1 good
And then I did some extra checks that were not in this TM:
K2-A1 to TP31 (25.90 VDC)
K2-A2 to TP31 when I try to start (0 VDC) Thinking K2 may be bad??? looked on flee bay could not find one?
Update: Found an K2 CONTINUOUS DUTY SWITCH RELAY SOLENOID 24 VOLT 4-TERMINAL HEAVY DUTY 1115615 Pretty sure it would work.
Note Gov Actuator does let go from the magnet target when I try to start with start switch
Question. Would be ok to jump 24 VDC to K2-A2 to see if the starter works? I could make a fused jumper???
There is alot of info in this site and you all seem to be very smart with these gensets. I have been doing alot and alot of reading in here before I decided to post.