Auxiliary panel question

epitts

Member
498
-1
18
Location
Terre Haute, Indiana
I picked up one of these panels Surplus Center - 120/240 VAC GENERATOR PANEL BOX to add to my MEP-002A. I open the panel up and it seems the wire color is all over the place. Red, Black, Green, Blue and Gray. How ever when I ohm out the panel it is using the Gray and Blue for power and the Green is ground, but Black and Red are wired as Neutral. My knowledge is limited on the spark side but I think I am right. See attached photo's and be nice!

Thanks for any help
 

Attachments

Triple Jim

Well-known member
1,386
320
83
Location
North Carolina
From what I can see in your photos, everything you said is correct. It even says "white" on the 30A receptacle where the red and black wires go in. Having red and/or black for neutral is very non-standard in the U.S.. I'd change them to white to avoid future problems, and would probably change the other colors to standard as well.

The terminals in the 30A connector appear to be the push-in type. I've had back luck with those, and regularly change to screw terminals whenever I come across them. The bad luck includes intermittent connections, and worse, a very hot outlet in one case, causing the plug to partially melt.
 
Last edited:

Triple Jim

Well-known member
1,386
320
83
Location
North Carolina
Excellent, then it's just a matter of wire colors. It is a bit odd that there's only one 30A 2-pole breaker on the panel, so that the 20A outlets are not limited to 20A.
 
Last edited:

epitts

Member
498
-1
18
Location
Terre Haute, Indiana
The way the panel is wired is one breaker feeds one side of the 240 outlet and one 110 outlet. The other breaker feeds the other side and one 110 outlet. Both breakers are 20 amp each. So you can run 110 or 240 but not both at the same time.

Thanks for the feed back
 

derf

Member
926
13
18
Location
LA
Over 20A on either breaker will trip it before too long but you can run a 240V load and a 120V load at the same time. For example if you had a well pump that draws 5 amps 240V and a 120V device that draws 5 amps you could run both.
 

epitts

Member
498
-1
18
Location
Terre Haute, Indiana
Over 20A on either breaker will trip it before too long but you can run a 240V load and a 120V load at the same time. For example if you had a well pump that draws 5 amps 240V and a 120V device that draws 5 amps you could run both.
So as long as the combined load is not over the 20 amps you are ok.
 

derf

Member
926
13
18
Location
LA
I think so. A balanced load is always better but a little unbalance shouldn't hurt.
For example, if you want to run two 9A 120V loads you can plug them both into the same outlet (using the panel in this thread as example) and it would work fine. But, the generator would be happier if you plugged on 9A load into each outlet so you would have 9A on each leg and therefore be balanced.

 

epitts

Member
498
-1
18
Location
Terre Haute, Indiana
Installed the panel

I installed the panel today using 6/4 SO cable. Ohmed the panel through to power lugs, all ok. Started it up, let it warm up, flip breaker NO SMOKE!! Pluged in my killOwatt 61.8 HZ and 121.5 Volts. All is good.:jumpin:

Thanks for the help!
 

epitts

Member
498
-1
18
Location
Terre Haute, Indiana
So far so good, attached is a video of ti in use. If you have more questions let me know.

[media]http://www.youtube.com/watch?v=hHrbwjzz3lk&feature=results_video[/media]
 
Top