Generators. Have a MEP 803A throwing a “OVER VOLTAGE “ light and shutting down . Does anyone have any suggestions on what is broke ? Possibly the voltage regulator? Part # 19580
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,964
6,430
113
Location
MA
Can you be more specific on details, like under what conditions it happens.. right after startup? After running a while? Have you performed any testing on items in the set related to this, or referenced the tech manual?
 

Captcday

New member
3
0
1
Location
Florida
At first it quit right after start up. We cycled the 1/3 phase switch a dozen times or so and it did start. We had it on a load bank at 7kw single phase and it ran for about 5 minutes. Then it quit again. Throwing the Over Voltage again.Do not know what to test. Also do not have a tech manual .
 

Daybreak

2 Star Admiral
Steel Soldiers Supporter
1,522
772
113
Location
Va
At first it quit right after start up. We cycled the 1/3 phase switch a dozen times or so and it did start. We had it on a load bank at 7kw single phase and it ran for about 5 minutes. Then it quit again. Throwing the Over Voltage again.Do not know what to test. Also do not have a tech manual .
Howdy,
Start here in this thread. The 2nd post has quick links to lots of stuff. The third post has links to the manuals.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,964
6,430
113
Location
MA
Yeah get the TMs first and foremost.
TM ending in -10 is an operators manual
TM ending in -24 is the troubleshooting manual
TM ending in -24P is exploded parts diagrams of everything that makes that machine up.

For troubleshooting purposes, almost EVERYTHING you could ever encounter, is covered by the -24. I think you have a corrosion issue, and I think you need to plan on purchasing a good contact cleaner, and taking the roof off the machine to get to the fun stuff.
 