gatorbob
Member
- 120
- 21
- 18
- Location
- Saint Augustine, FL
Passing this along for anyone who hasn't installed a permanent meter yet.
I had a hard time finding a single meter that would measure current in amps on both legs, voltage, *and* frequency. I found one by NoOutage.com called the PowerMeter 6 (NGV25-SW). It can also show the Power Factor, Total Operating Time on generator, and the load in kW.
It's basically a 3 gang box, meter with LED display, display switch for L1/L2/Total, and a pair of CTs. You can buy a second set of CTs for the utility power but I didn't want/need the extra expense. I paid $220 for the unit with a single pair of the smaller split CTs (24 kVA rated). It was more than I wanted to spend but it's exactly what I wanted and it I was able to support a small business here in the US.
It requires 240V power and the instructions call for using the generator feed. I used some taps and put them on the feeder cables before the breaker so I can check the frequency and voltage before switching the load to the generator.
Here are some pics. I forgot to take a picture of the 2nd display mode with kW, hours, and PF.



I had a hard time finding a single meter that would measure current in amps on both legs, voltage, *and* frequency. I found one by NoOutage.com called the PowerMeter 6 (NGV25-SW). It can also show the Power Factor, Total Operating Time on generator, and the load in kW.
It's basically a 3 gang box, meter with LED display, display switch for L1/L2/Total, and a pair of CTs. You can buy a second set of CTs for the utility power but I didn't want/need the extra expense. I paid $220 for the unit with a single pair of the smaller split CTs (24 kVA rated). It was more than I wanted to spend but it's exactly what I wanted and it I was able to support a small business here in the US.
It requires 240V power and the instructions call for using the generator feed. I used some taps and put them on the feeder cables before the breaker so I can check the frequency and voltage before switching the load to the generator.
Here are some pics. I forgot to take a picture of the 2nd display mode with kW, hours, and PF.