how many KVA is my MEP 002A

justacitizen

Active member
408
40
28
Location
oklahoma
I am no expert so let me know if i figured this correct. to figure the KVA of my MEP 002A i first took 240 volts x 26 amps x 1.732 constant then divided by 1000 240x26x1.732 divide 1000 =10.80 so my little 002a is 10 kva? right?
 

justacitizen

Active member
408
40
28
Location
oklahoma
I think i need to re word this post. I am in agreement with Chainbreaker. i just posted the caterpillar link to show where and how i made my error. I knew the set couldn't be a 10 kva.


this makes more sense! i was using the formula provided by caterpillar on their power generation websight. here https://www.cashmanequipment.com/UserFiles/Uploaded/cms/generator-power-factor.pdf




kW to kVA calculation formula

The apparent power S in kilovolt-amps (kVA) is equal to the real power P in kilowatts (kW), divided by the power factor PF:

S(kVA) = P(kW) / PF

Source: http://www.rapidtables.com/calc/electric/kw-to-kva-calculator.htm

So for single phase AC 5 kW/.8 PF = 6.25 kVA
 
Last edited:

Isaac-1

Well-known member
1,970
51
48
Location
SW, Louisiana
You will see that these units are VERY conservatively rated, for example output is rated 24x7 at around 120 degrees F (depends on the model) and up to 5,000 ft altitude without derating where commercial units are generally rated at 86 degrees F and under 1,000 ft altitude, they are also generally rated as standby or maybe prime power rating, both limit runtime (standby is usually limited to 500 hours per year) as well as limit percentage of time at full output.
 
Top