how to excite a 3kw onan MEP-016A genset

Boatcarpenter

New member
1,877
17
0
Location
Marlborough, NH
From TM 5-6115-271-14
Flashing the field without a switch
1. open or remove control box cover
2. Connect two 1.5 volt batteries in series and connect a wire to each end.
3. connect the positive wire from the batteries to terminal No. 20 on the voltage regulator.
4. start the generator set
5. momentarily touch the negative wire to terminal No.21 on the voltage regulator to flash the field.

Good Luck,
BC
 
Last edited:

dirtyfingernails

New member
778
4
0
Location
Gainesville, FL
Sometimes the field has to be flashed. This can be done after it is running by rotating the starting switch to "start" AGAIN. I have a Mep003 that requires this everytime I run it. My other doesn't need the flash. Just my experience.
 

BKubu

Well-known member
Steel Soldiers Supporter
4,755
1,146
113
Location
Gaithersburg, MD
Lance, I swear I was thinking the same thing...something about removing the quiet pack from a 10KW genset to excite the little guy, but I hesitated...! :wink:
 