Makes enough sense for what I’m doing. If you get too in depth my eyes will glaze over and you’ll just be exercising your thumbs.
Can the main breakers be used for wire protection?
Thanks for the laugh. My thumbs don't need more exercise.
That is a bit of a "have you stopped beating your wife yet?" question to me. If the breakers are sized appropriately, then yes! That's the point. Breakers and fuses are there to protect the wires at a minimum, and perhaps also the devices on the circuit. Bad things like fires happen if wires get overloaded, and speaking from experience fires in walls are tough to fight and do lot of damage.
Unlike
@Guyfang and others, I am not a certified electrician, so don't rely on my electrical advice.
You can put slightly heavier (larger) wires on a circuit, but each breaker will have an upper limit of the size (gauge) of wire and temperature limits that it will take, there are ampacity charts and calculators available. So, don't expect a 100A breaker to protect your generator. For short distances, 6AWG copper wire or cable probably would be sufficient for 50A loads. If you plan on pushing the limit for hours at a time, 6 is probably not sufficient unless you also upgrade the wiring (either gauge or temperature rating, or both) to tolerate higher temperatures.
The purpose of this calculator is to determine the ampacity of conductors in conduit, cable, or directly buried. All calculations are based on the National Electrical Code®.
www.cerrowire.com
Voltage drop becomes important when the length of a run of wire or cable becomes very long. Usually this is not a problem in circuits within a house, but may become an issue when running wire to an outbuilding, well pump, etc.
www.cerrowire.com
Mil-spec cable tends to be significantly higher specification with respect to temperature ratings, and usually more resistant to oil/diesel fuel, the latter of which has a tendency to degrade many types of insulation.
I think that
@Scoobyshep makes some good points about the potential fallibility of the generator breaker. There are enough reports of issues that I would not rely on it to save your bacon. Circuit breakers have a limited lifetime, and in home usage, home inspectors start recommending replacing them after twenty years or so. Most of these generators are past that age.
Electric circuit breakers come in various sizes and types and protect your home's electrical system by monitoring and shutting off electricity when problems
homeinspectioninsider.com
I have zero personal experience running lifetime studies on mil-spec breakers, but anecdotally there seem to be mil-spec breakers that lived up to expectations and some that didn't. I defer to folks here with more hands on experience.
All the best,
2Pbfeet