SUBJECT: Maintenance Advisory Message No. 88-01, Clarification of receptacle rewiring procedures, 5/10KW DED generators, MEP-002A, MEP-003A
A. Technical Manual (TM) 5-6115-584-12
B. TM 5-6115-585-12
C. Technical Bulletin (TB) 5-6115-584-30-1
D. TB 5-6115-585-30-1
E. TB 5-6115-584-30-2, dated Aug 26, 87
F. TB 5-6115-585-30-2, dated Aug 26, 87
G. MILNET Msg. AMSTR-WLT, 5 Jan 88, SAB
H. Maintenance Advisory Message 87-41
1. This is a maintenance advisory message and has been transmitted to affected units under your command. please ensure dissemination of this message to all applicable using units.
2. Ref. C, D, and G (above) notified the field that convenience recepticals (CR) should be disconnected because of problems with more than expected voltage at the CR when the gen set is placed in the 120/240 volt single phase mode and less than full expected voltage at the CR when the gen set is placed in the 120 volt single phase mode.
3. CR wiring must be carefully inspected prior to proceeding with wiring changes. Some CR's may have been re-wired and later disconnected, and some may have never been changed.
4. After inspection following the procedures of Ref. E, F and H (above),
First, connect CR as outlined in applicable TB (Ref. E or F) paying special attention to paragraphs 98 (7) thru (12).
NOTE 1. Dependent on the manufactured configuration of the generator, the instructions of para. 98 ( 8 ) and (9) or para. 98 (10) and (11) are followed. Where para. 98 ( 8 ) and (9) apply, there may be some deviation in locations of terminals on the switch from the instructions in the message.
Second, connect the jumper (AWG Nr 4) between L0 and NR. 6 of section 9 as outlined in ref. H.
NOTE 2. Terminal nr. 6 of section 9 is located on the 10th ring (the first ring is a cover, count from the control panel end) of the switch. The correct terminal will have wires X6A8 and X6B12 attached. Wire number X6B12 was added during performance of TB instructions. You may encounter wires with old markings (X12L12) or incorrectly marked conductors at this location.
L0 is located on top of the switch at 11th, 12th, and 13th rings of the selector switch with wire X13B8 connected to the 13th ring with bare copper jumpers from rings 13 to 12 and 12 to 11.
5. Re-assemble and check for proper operation IAW applicable TM and the following:
1). Close CB-3 (CR circuit breaker)
2). During operation and in each position of the reconnection switch, you should have zero (0) volts AC between the CR neutral terminal (wide slot) and ground (gen set frame) or the CR grounding terminal (U shaped).
3). During operation and in each position of the reconnection switch, you should have 120 VAC between the line terminal ("hot" - narrow slot) and the neutral terminal (wide slot) of the CR or the CR grounding terminal (U shaped).
6. The reconnection will only be accomplished at intermediate level maintenance.
7. Change to the above TMs, ref. A and B (above) will be distributed 3rd qtr FY88.
8. Addressees will confirm receipt of message to this office, if applicable. Point of contact at this command is Mr. Dave Long.