Need an ac circuit interrupt switch for my memo-803a 10000 watt diesel generator
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
DefectiveIs yours missing, or have you tested it to be nonfunctional?
It was working and just stoppedDefective
8906K4519 | 2TL1-70 |
1 | 3 |
2 | 2 |
3 | 1 |
4 | 6 |
5 | 5 |
6 | 4 |
Does not go on at all but if I push it in to test the light goes onWhen you lift the switch UP and hold it up does the green contactor light illuminate?
Does it then go out when you release the switch?
These switch's seldom go bad so I'd suspect the issue with the contactor not closing is due to something else.
Not handy but I can pick one upDo you have a hand held meter available to do DC voltage measurements?
Nope the light stays out no matter that I do it will go on if I push it in to test it onlyWhen you lift the switch UP and hold it up does the green contactor light illuminate?
Does it then go out when you release the switch?
These switch's seldom go bad so I'd suspect the issue with the contactor not closing is due to something else.
Thanks I will do that anyone know an electric generator mechanic in New York Long Island area ?????This may sound like a odd solution but, it sounds like your K1 is hanging up internally.
If you have already measured things per the TM using a meter, that means you have the top cover off and K1 exposed.
Go in there and tap sharply on K1 with a rubber mallet or something a few times, than fire up the machine and try the circuit interrupt switch again.
I can't count how many I have fixed this way.... and a few others here have done it successfully as well.
If it works you may want to consider opening up the contactor to see if there is come corrosion or something in there causing it to stick.
It's a very simple magnetic solenoid and the mechanical motion of the solenoid pulling down activates an internal switch which illuminates the panel light.