I would say that is a little more droop than optimal, you can probably tune it a bit better, but it is probably close enough for reasonable operation.
Ike
Ike
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
I would have sworn I answered this question a few hours ago, perhaps on another thread. I have no more hair to lose, but I did sort it out by stopping doing as you are doing....even worse, I tend to fool with 3-4 adjustments at once. Finally went to the TM and did the governor adjustment by the book. All is well. 2 cycles droop is fine.I was just curious if: 1) you fixed your machine , 2) what did you find and 3) Has your hair since grown back or is this generator continuing to cause you trouble?
Thanks
Ray
That's a really good way to checkRay70. If your drooping that far you likely have other issues. Quick check.
If you load it down and its at max droop go push the throttle arm up. If it is maxed out already the governor is fine, and you have fuel issues. Likely injector spray or pressure issues.