Another way of load testing can be done very cheaply. It is not for the faint of heart but if you are flipping load switches anyway you are not too far from the hot source....
I have used this method for testing gensets to full load at 40 kw
Fill a PLASTIC garbage can with tap water, about 20 gallons for a 10 kw genset.
Don't make a mess!
Put 2 rods, can be 1/2 pipe, on opposite sides, vertical, full length of the container, (in the water ) clamp in place
Connect #8 THHN 90 C wire from one phase of the 220 genset output to one rod and the second phase to the other rod for a 10kw or smaller genset.
Now you have 220 potential between the rods but will have little current flow even if you used tap water.
Connect an amp probe on one of the wires, use a known accurate one to check against the genset amp meter / load meter
Start the genset and warm up
Note the amp reading
Start adding common table salt between the rods and note the amp readings
Load will increase with salinity
2~ 2 quarts of salt will do about 175 amps in 30 gallons of water so 1 quart or less of table salt should be plenty for 10 kw
Open breaker when done testing (load test on breaker)
Dilute and do over if needed....
Notes;
Water will get hot and steam
Don't touch the water
Adding salt slowly will increase the load gently
I have used this method for testing gensets to full load at 40 kw
Fill a PLASTIC garbage can with tap water, about 20 gallons for a 10 kw genset.
Don't make a mess!
Put 2 rods, can be 1/2 pipe, on opposite sides, vertical, full length of the container, (in the water ) clamp in place
Connect #8 THHN 90 C wire from one phase of the 220 genset output to one rod and the second phase to the other rod for a 10kw or smaller genset.
Now you have 220 potential between the rods but will have little current flow even if you used tap water.
Connect an amp probe on one of the wires, use a known accurate one to check against the genset amp meter / load meter
Start the genset and warm up
Note the amp reading
Start adding common table salt between the rods and note the amp readings
Load will increase with salinity
2~ 2 quarts of salt will do about 175 amps in 30 gallons of water so 1 quart or less of table salt should be plenty for 10 kw
Open breaker when done testing (load test on breaker)
Dilute and do over if needed....
Notes;
Water will get hot and steam
Don't touch the water
Adding salt slowly will increase the load gently