MEP 002a Thermo Power Unit (Activates Shutters)

Keith_J

Well-known member
3,657
1,323
113
Location
Schertz TX
Update:

Put it all back together and set the cold operation slide off.

Shutters opened this time exactly as I expected at the temperatures I measured (> 120 degrees). They did not before, and I think this was the real cause.

I think only time will tell now, I need a real outage, or for the family to head out for a while one day and I'll test it under a good solid load. I think it's going to be fine now, I really should not have run it with the cold setting on the air filter, I'm sure that was a contributing factor, as well as the shutters sticking being IMO the main cause.


Thanks for all the help!
I run mine with air preheat to help it warm up. Shutters only fully open with a good load like my welder.
 