mep 003 no power output, disconnected battery while running.

bchauvette

New member
807
5
0
Location
Easley SC USA, 29640
All of a sudden my MEP 003 stopped putting out powerAlso No power to the convenient outlet. The set came with a battery disconnect switch. I just realized After many days of searching the TMs that I I may have been disconnecting the battery while running. I've been scouring through the TMs looking for the stuff on servicing the rectifier bridge with no luck. If someone could point me to the TM number and location that would lead me to troubleshooting no power output. I would appreciate it. So the basic question is What are the diagnostic steps when there is no what power output.Sorry for the bad grammar. My stroke has left my brain scrambled. Among other things.

Thank you in advance

Butch M944A1, Mep 003,sold the Mog ( kermit)
 

kloppk

Well-known member
Steel Soldiers Supporter
2,254
3,948
113
Location
Pepperell, Massachusetts
TM5-6115-585-34 has a section on troubleshoot.
Page 2-9 in the July 1977 version of the TM.

If you have the PDF you can search for... ENGINE RUNS NORMALLY BUT GENERATOR HAS NO OUTPUT
 

Guyfang

Moderator
Staff member
Moderator
17,453
25,817
113
Location
Burgkunstadt, Germany
Before you go into the rectifier bridge, lets start at the beginning. Could be simply the S1 start switch. Or something simple.

Will the set start and run correctly? Do you have voltage at the load terminals? The 120 volt outlets are separate from the load terminals. You need to see if there is voltage there also. Does the set volt meter and frequency meter read right? If so, your set puts out power, just need to see why the 120 volt outlet doesn't work.
 

doghead

4 Star General /Moderator
Staff member
Super Moderator
Steel Soldiers Supporter
26,246
1,184
113
Location
NY
The first sentence in the first post said he had no power at the convenience outlets.
 

Chainbreaker

Well-known member
1,820
2,080
113
Location
Oregon
Also, after checking Guy's start the easy diagnostics...have you checked the F1 (alternator fuse) and are you able to cycle/exercise the AC Voltage Reconnect switch?
 