chiefgguy
New member
- 16
- 1
- 3
- Location
- Magnolia, TX
Team SS!
I find myself again needing some guidance to getting my MEP back up and running .. The unit has been running great for the past several years, we use it predominately on weekends to run an off-grid cabin.
I've reviewed several the threads on the site and have tried some of the steps but still no joy..
About 3 weeks back, we ran into an issue where it would not "start" by that I mean the starter is not "engaging" to turn over the unit. There is a mechanical "click" from the right of the unit where the plunger engages under the solenoid, beyond that there is no further "noise" or "action". We've taken the following actions:
- Checked the batteries they test good, but went ahead and charged them up while we had them out.
- Checked the starter solenoid/starter - we can short a screw drive across and it "functions"
-Checked power at the solenoid for the fuel shutoff and we have power there (the plunger does actuate when we try and start)
- took the cover off the starter lockout (just below the fuel solenoid) and it remarkably clean in there.
Today we setup a manual switch connected to the solenoid / starter, and manually press the plunger up (on right under fuel solenoid) and we can get the unit to run (although I have manually to continue working the plunger). Once I let go of the plunger the unit stops.
We think it's a power problem since we can get the unit to start, but not sure how to further diagnose. Any suggestions or ideas are welcome!
thanks - Andy
I find myself again needing some guidance to getting my MEP back up and running .. The unit has been running great for the past several years, we use it predominately on weekends to run an off-grid cabin.
I've reviewed several the threads on the site and have tried some of the steps but still no joy..
About 3 weeks back, we ran into an issue where it would not "start" by that I mean the starter is not "engaging" to turn over the unit. There is a mechanical "click" from the right of the unit where the plunger engages under the solenoid, beyond that there is no further "noise" or "action". We've taken the following actions:
- Checked the batteries they test good, but went ahead and charged them up while we had them out.
- Checked the starter solenoid/starter - we can short a screw drive across and it "functions"
-Checked power at the solenoid for the fuel shutoff and we have power there (the plunger does actuate when we try and start)
- took the cover off the starter lockout (just below the fuel solenoid) and it remarkably clean in there.
Today we setup a manual switch connected to the solenoid / starter, and manually press the plunger up (on right under fuel solenoid) and we can get the unit to run (although I have manually to continue working the plunger). Once I let go of the plunger the unit stops.
We think it's a power problem since we can get the unit to start, but not sure how to further diagnose. Any suggestions or ideas are welcome!
thanks - Andy