Hi Folks,
My mep-004 w/ask is tripping the 7.5 amp dc breaker after I close the a/c breaker to my building. Takes a few seconds then the breaker pops and the unit stops running. Restarts after resetting.
Can anyone think of a common problem these machines have?
After about 50 hours of use on a 1100 hr machine. I have replaced the fuel pumps, and need a day tank switch. Day tank failed the test in the manual, I checked this after finding the original pumps burned out. Machine has run maybe 20 hours since new fuel pump. I have done a visual inspection for shorted wires, found none. I haven't removed the special relay box to do an inspection though, looks like a pain. Any issue's with these due to vibration?
I wish there was a deep sea retrofit so I could get rid of allot of the obsolete hardware.
Thank you in advance for any help guys.
Regards, Mattell
My mep-004 w/ask is tripping the 7.5 amp dc breaker after I close the a/c breaker to my building. Takes a few seconds then the breaker pops and the unit stops running. Restarts after resetting.
Can anyone think of a common problem these machines have?
After about 50 hours of use on a 1100 hr machine. I have replaced the fuel pumps, and need a day tank switch. Day tank failed the test in the manual, I checked this after finding the original pumps burned out. Machine has run maybe 20 hours since new fuel pump. I have done a visual inspection for shorted wires, found none. I haven't removed the special relay box to do an inspection though, looks like a pain. Any issue's with these due to vibration?
I wish there was a deep sea retrofit so I could get rid of allot of the obsolete hardware.
Thank you in advance for any help guys.
Regards, Mattell