MEP-016B/701A Main (A/C) Circut Breaker tripping with no load

Valence

Well-known member
Steel Soldiers Supporter
2,112
555
113
Location
Davis County, UT
I would appreciate a little help diagnosing the problem of me not getting power on the output terminal and the Main A/C Circuit Breaker tripping with no load:

My 1986 MEP-016B (with ~784 hours) starts and runs great, even after a long period of sitting.
I have my generator configured in the inside panel to be 120/240V Single Phase.
Voltage Selector on V1-0
Current Selector on I-2

If the Main A/C Circuit Breaker is in the "OFF" position, I get a voltage reading on the convenience receptacles that matches the panel "AC Volts" meter. I can adjust the voltage via the Voltage adjust knob and I can adjust the frequency displayed on the Hertz meter with the Manual Speed Adjustment knob. As expected with the Main AC Circuit Breaker in the "OFF" position, there is no voltage reading on the terminal/lugs on the right side (well, there is but it's only about 0.2V).

2022-02-06 18.05.46.jpg

However, I am unable to move the main AC Breaker to the "ON" position. Attempting to do so you can visually see the spark of the trip through the clear rubber cover and hear the motor skip a step.

I can actually start the generator with the Main A/C Circuit Breaker in the "ON" position and it will stay there, but I will get the same ~0.2v reading on the convenience receptacles. The AC Volts and Hertz meters will read zero.
2022-02-06 18.08.58.jpg

If I flip the Main A/C Circuit Breaker OFF, the AC Volts and Hertz meters will come to life and I get the proper voltage reading on the convenience receptacle. This behavior can be seen in this very short video I took:


I have performed all the trouble shooting that I could find in the TM 5-6115-615-12 - 062759 Operators & Maintenance Manual:

Section 3-3 Troubleshooting, #7 is "GENERATOR SUPPLIES NO VOLTAGE TO LOAD" but the instructions aren't very helpful as I am "higher echelon maintenance" for my poor generator. and I don't have anything connected yet, I am just trying to get 120V reading on each L1 & L2 (since I have it in the 120/240v single phase operation)
02_No_Voltage_To_Load.JPG 03_No_Voltage_To_Load.JPG

Section 3-35.5 instructs to inspect the Main Circuit breaker and connections. All connections on the back of the circuit breaker on the inside were very secure, and I could see no physical damage any other markings indicating an issue (melting, etc)
04_Inspect_Main_Circuit_Breaker.JPG

Section 4-2, part 8, instructs to check the load for a short circuit, but again, I don't have a load connected at all to it yet as I was just trying to get the voltage to read on the terminal/lugs first.
05_Main_Circuit_Breaker_Will_Not_Close.JPG

Finally, section 4-70 has me label each of the wires and remove the circuit breaker and test it, which I have done.
06_Test_Main_Circuit_Breaker.JPG 07_Test_Main_Circuit_Breaker.JPG 2022-02-07 22.25.27.jpg 2022-02-07 22.25.43.jpg
The side of the main circuit breaker reads:
72-169-2-MG6
__________P1P2_____P3
AMP _____35_______ 20
VOLT_____250______250
HZ______50/60____50/60
Delay______P________ P
Line
13208E5838-1
PAM333-MG6

I followed the above instructions and my results were as follows:
When the circuit breaker was in the "OFF" position, A1-B1, A2-B2, and A3-B3 showed higher resistance than my Fluke Multimeter could read (aka Open Circuit) (it was actually an open circuit between all the pins).
When the circuit breaker was in the "ON" position, A1-B1, A2-B2, and A3-B3 each read ~0.3-0.4 ohms, and open circuit between all others.

The TM says there should be a zero ohm reading between the pairs of pins (A1-B1, A2-B2, and A3-B3) when in the "ON" position. 0.3-0.4 ohms is not zero but it also is not very much resistance. Is the circuit breaker O.K. then or should it be replaced? I don't know what else to check.
(if needed, I do have 2 other MEP-701A generators that DO work as expected and I could borrow their Main Circuit Breaker)

Thank you very much!
 
Last edited:

Scoobyshep

Well-known member
1,158
1,572
113
Location
Florida
Try this, with the breaker off and the generator not running, check the resistance of the output terminals to each other and to ground. You may have a wiring fault downstream of the breaker. The spark and motor skip has me suspecting a short.
 

Guyfang

Moderator
Staff member
Moderator
16,896
24,462
113
Location
Burgkunstadt, Germany
Try this, with the breaker off and the generator not running, check the resistance of the output terminals to each other and to ground. You may have a wiring fault downstream of the breaker. The spark and motor skip has me suspecting a short.
Another way to check this would to be disconnect the output wires on the CB. Start the set, then try and close the CB. If it pops, then you know the problem is from the CB.
 

Valence

Well-known member
Steel Soldiers Supporter
2,112
555
113
Location
Davis County, UT
Another way to check this would to be disconnect the output wires on the CB. Start the set, then try and close the CB. If it pops, then you know the problem is from the CB.
Great idea. I appreciate an additional way to verify that the circuit breaker is good. I reconnected the Main Circuit Breaker, A1, A2, & A3 side only ("Line" side) with the 'B' side ("Load" side) not connected. I started the generator and the circuit breaker did not trip when moved from "OFF" to "ON".

Try this, with the breaker off and the generator not running, check the resistance of the output terminals to each other and to ground. You may have a wiring fault downstream of the breaker. The spark and motor skip has me suspecting a short.
You were correct and the problem was indeed downstream. I had a thought last night that I should check the terminals again, and low and behold, the TM was right. The problem was at the "Load". The clips on the L1 & L2 terminals (each at 120v) had managed to touch each other and were short circuiting. *SIGH* Least it was fixed easily.

2022-02-08 13.18.59.jpg 2022-02-08 13.25.06.jpg
Only a little bit of damage occurred to the clips - I assume I can find replacements from somewhere?

Circuit breaker stays on now after startup. Thanks you guys!

Video of it working:
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
16,896
24,462
113
Location
Burgkunstadt, Germany
Review the attachments. No you can not buy them. This is such a HUGE problem in the Army, that every few years, this notice comes out in the PS Magazine. When I was a young soldier, I took them off and tossed them. When I was the boss, and responsable for the results of a Maintenance inspection, I made these darn things. I always felt like they were crap. Every generator section I ever saw, had a large container full of terminals, without clips, since the only way to get a new one was to order a whole terminal.
 

Attachments

Valence

Well-known member
Steel Soldiers Supporter
2,112
555
113
Location
Davis County, UT
Hah, welll, hey I can use that info regardless because, as you can see, the top terminal doesn't have a safety clip at all.
 