MEP-016D Connections

Stob

New member
14
0
1
Location
VA
What function does L0 have? The manual says to connect to L1 and L2 for 120V single phase. Which is the neutral? 120V 3 phase uses L1, L2, L3, OK with that.120/208 3PH 4 wire connects to all 0,1,2 and 3.

So is L0 a ground? A neutral isn't needed for 3ph.
 

Crawdaddy

Member
444
4
18
Location
Louisiana
The MEP-016 family of gensets are weird. If I remember correctly, L2 is the neutral in a 120V 1ph setup. L0 is only used in 3 phase operation. Also, beware of the connections diagrams in the TMs. They have some inaccuracies in them.
 

Stob

New member
14
0
1
Location
VA
I have a the manuals, don't recall an actual "wiring connection" diagram. B it there is a page which shows a photo of the 4 lugs, and describes where to connect to for a given application, which is where I got the info for my post. But what it DOESN'T say is which is the neutral. Things now days seem to like the polarity proper.
 

Crawdaddy

Member
444
4
18
Location
Louisiana
I'm referring to the TM for the MEP-016B which is very similar to your MEP-016D, but the two manuals may vary slightly. There's a section that describes grounding and illustrates what lug to bond to ground. That's how I determined which lug is neutral. It's section 2-5.1 in the B manual.
 

Isaac-1

Well-known member
1,970
50
48
Location
SW, Louisiana
The problem here is when you are generating 120V only on a generator the concept of neutral is relative. You are in reality generating 120V line to line, this is not exactly the same as the 120/240V split single phase power that comes into most homes. You can designate one of these 120V lines as a neutral and ground it, from the generators perspective it does not care which one you pick, just make sure you don't ground both, check for a frame grounding strap on the back side of the lugs (inside the box).
 