• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP-1040 Fault 2335 "Excitation Fault"

peapvp

Well-known member
Steel Soldiers Supporter
1,081
1,161
113
Location
Basehor, KS
Check wiring from A1 P1 J K to P90 J90 1; 2 to F1 and F2
Connect DC meter and on J90 1; 2
start Genset
at 600 rpm watch DC Meter on J90
If there is no DC then A1 needs to be repaired.
A1 contains exciter / AVR

Peter
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,759
5,712
113
Location
MA
This item is not in my possession. Available semi-locally and the guy is asking way too much for its current non generating 'paperweight' state. Was doing some preliminary investigating.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks