since you have no load attached to it, your % load gauge is not going to move. As Bob said, the frequency gauge could be messed up a little bit, check the transducer and gauge for loose and/or dirty connections, It's a VERY common problem with the frequency meters. If you have a good electrical multimeter, you may have a frequency setting on your multimeter. Use the convenience receptacle on the front of the set with your multimeter and set the speed using the frequency setting of your multimeter.
As for the voltage gauge not showing anything...you sound like you are very new and unfamiliar to these sets. Are you sure you have the amp/voltage/phase selector switch in the correct position to read the voltage from the proper phases? There is a selector switch that looks just like the start switch...it is located on the right side of the control panel. If you have the large "output reconnection switch" (located under the metal flap beside the main breaker) set for either 120 volt single phase or 120/240 volt single phase operation you'll not see any voltage on the volt meter unless that smaller selector switch is in the proper position. For either of the single phase operations, you'll need to have it in one of the two extreme clockwise settings...if you look at the markings around the switch you'll notice that these two clockwise positions are for the single phase output setting. This switch reconnects the metering devices of your set to give you proper metering depending on how you have the generator configured to run.
All of this information is in the TM as Carl mentioned.
As for the voltage gauge not showing anything...you sound like you are very new and unfamiliar to these sets. Are you sure you have the amp/voltage/phase selector switch in the correct position to read the voltage from the proper phases? There is a selector switch that looks just like the start switch...it is located on the right side of the control panel. If you have the large "output reconnection switch" (located under the metal flap beside the main breaker) set for either 120 volt single phase or 120/240 volt single phase operation you'll not see any voltage on the volt meter unless that smaller selector switch is in the proper position. For either of the single phase operations, you'll need to have it in one of the two extreme clockwise settings...if you look at the markings around the switch you'll notice that these two clockwise positions are for the single phase output setting. This switch reconnects the metering devices of your set to give you proper metering depending on how you have the generator configured to run.
All of this information is in the TM as Carl mentioned.