Since you have a 3 wire feeder to your sub panel in the barn things will be a little more complicated. The code changed in the 2014 edition.I read this page: http://www.esgroundingsolutions.com...eutral-and-the-ground-wire-in-the-main-panel/
I will ask the local electrician for input of course, but as I understand the neutral and ground may need to be bonded at the generator in my case.
Per the 2014 edition of the code you should bond the neutral and ground buss in the sub panel as long as there are no other possible ground paths back to the house (cable tv line, metallic conduit, metal water pipes). In this case you would leave the neutral and ground unbonded at the generator and bond them at the sub panel. You can use a breaker interlock with that configuration and be OK.