• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP 802a. ran without a ground rod. Gen set putting out fine but current isn't making it to out put wires. what is wrong?

flyfishtrailer

Well-known member
Steel Soldiers Supporter
554
1,041
93
Location
Cool, CA
Have you checked the internal volts/phase dial matches the external dial? Also, assuming the AC interrupt switch has been switched and you have a green light indicating power is now at the lugs? And seeing your new to SS, have you downloaded the technical manuals (TM's) for the MEP803 in the TM section for generators? And lastly, welcome to the addiction.
 

Grub

New member
4
7
3
Location
South Carolina
Thank you both for the replies. Still black dark here in SC.....Will follow up on your suggestions during daylight hours. Engine running fine, gauges show normal electric output. No power coming out of the AUX 110V receptacle or the out put lugs. Many TKS
 

Ray70

Well-known member
2,592
5,907
113
Location
West greenwich/RI
The lugs and receptacle are on 2 separate circuits in a sense. if the generator is showing power on the gage and no output from the receptacle, first thing I'd check is the GFCI reset on the face of the breaker.
If that is not tripped, then check the circuit breaker switch for the receptacle inside the control panel on the left side of the panel opening.
I'd suggest troubleshooting the receptacle first and the lugs 2nd.

Also, please tell us answers to all Guy's questions.... that will point us in the right direction, especially the last question, does the green light above the AC circuit interupt switch illuminate then you push up on the switch AND does it illuminate when you press in on the face of the light itself ( bulb test function )
 

Grub

New member
4
7
3
Location
South Carolina
Thank you & others for your suggestions. I have not been able to try the various "fixes" suggested but will reply in full as soon as I have tried them all or until it is again working properly. I am not at all familiar with these gen sets nor am I very good as a mechanic. I do not feel that there is anything really wrong with the mechanics of the set......The real problem is my going up a very steep learning curve. I also feel that with the help I am getting from y'all the problem will be solved. Many TKS.....Grub
 

Grub

New member
4
7
3
Location
South Carolina
Thank you again. #1. It starts & runs fine.....always has
#2. No fault lights after starting & running
#3. AC voltage is showing on the M 1 AC Volt meter
#4. Yes there is 120 volts at the J1 receptical...I ran a angle grinder from it for
#5. Yes I did push it up then down
#6. Yes the DS7 did come on
I think all is well now. What led me to believe that is wasn't working was the fact that the J1 receptical was not working but it had been earlier. I think I am OK now & I thank both of you very much.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks