MEP-802A Starter problem?

rcamacho

Well-known member
770
844
93
Location
Bainbridge Island Wa
I'm getting into seasonal maintenance a tad late.
MEP-802A is acting up a tad. The starter will kick in briefly and then stop when the switch is engaged. Dead crank has no problem engaging the starter continuously. I presume this is a bad solenoid or start relay somewhere. Where do I start in the TM for diagnosis on this?
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
276
63
Location
Eubank, KY
I'd start with the schematic on the door of the unit.

Identify the parts involved in cranking the engine and check the wiring for accuracy and soundness of connections.

If the dead crank switch will engage the starter without the starter dropping out, your problem is not the starter or starter solenoid, it is more likely a switch or relay further back in the circuit.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,829
5,945
113
Location
MA
As Farmitall said, if DC kicks it over without issue its in the other circuitry. I would take the top off and inspect/clean the crank relay. A very simple assembly you can hit with some deoxidizing cleaner when you take the small plastic/ceramic top off it.
 

Ray70

Well-known member
2,595
5,912
113
Location
West greenwich/RI
In addition, verify your batteries are fully charged.... , despite being able to crank from the dead crank switch, low batteries can still cause this same problem.
The starter pulls so much amperage that it can cause the cranking relay / starter disconnect relay inside the control cube to open almost instantly if the batteries are low due to the starter motor drawing down the available voltage.

The dead crank switch bypasses the relays sending power to the start solenoid through a different path.
 

kloppk

Well-known member
Steel Soldiers Supporter
2,145
3,526
113
Location
Pepperell, Massachusetts
In addition, verify your batteries are fully charged.... , despite being able to crank from the dead crank switch, low batteries can still cause this same problem.
The starter pulls so much amperage that it can cause the cranking relay / starter disconnect relay inside the control cube to open almost instantly if the batteries are low due to the starter motor drawing down the available voltage.

The dead crank switch bypasses the relays sending power to the start solenoid through a different path.
Attempting to start via S1 also engages the Preheaters which draw a lot of power. When dead cranking the preheaters are not powered.
 

kloppk

Well-known member
Steel Soldiers Supporter
2,145
3,526
113
Location
Pepperell, Massachusetts
After you verify your batteries are good and fully charged...

To help isolate the cause of the starter dropping out you could measure the DC voltage at relay K16 terminals 6 & 9 with respect to chassis ground.
Both terminals should have about 24 volts DC on them when cranking.
If both have 24 volts on them and them when the starter stops then issue may be with the K2 starter relay.
If you only have 24 volts on terminal 9 when the starter stops then issue may be with S14 or the MPU.
If you don't have any DC voltage on either terminal when the starter stops then issue may be with a fault being generated by the fault monitor.

Here are the terminal locations on all the relay sockets.
Relay Socket.jpg
Here are the relay locations
Relays With Labels.jpg
 

rcamacho

Well-known member
770
844
93
Location
Bainbridge Island Wa
Disregard,
MIP is functional and starter is no longer dropping out. Why? Not sure. All I did was look at FU1, and circuit breakers for MIP and DC.
Going through PMCS now. Replacing fuel filters and oil service. Air filter is fresh/clean.
 

rcamacho

Well-known member
770
844
93
Location
Bainbridge Island Wa
Fuel filter and oil PMCS completed.
Waiting on water separator part.

Generator is acting like it has no gel fuel delivery.

Fuel shut off solenoid is pulsing position off of stop on cranking. Tried running the fuel rail by hand during cranking-no difference.

Next up is checking low pressure feed to the injectors then output on the high pressure side.


Sent from my iPhone using Tapatalk
 
Last edited:

Ray70

Well-known member
2,595
5,912
113
Location
West greenwich/RI
No Gel delivery and your fuel shut off solenoid is pulsing....?? Gotta love speech to Text!
So is the shut off solenoid pulling back and holding steady when cranking or are you seeing an issue with it bouncing ( pulsing ) back and forth?
Hard to tell what you said Vs. what your phone thinks you said!

Check fuel delivery to the metering pumps.
TM gives a fuel delivery / time spec. but if you have the cube style fuel pump they typically die ( but still sound like they are working ) and deliver no fuel.
This is assuming your primary pump is in fact making noise? ( you should hear the primary pump when in the prime / run position on the start switch.
 

rcamacho

Well-known member
770
844
93
Location
Bainbridge Island Wa
Lovely job Siri... ;)
Fuel stop solenoid is pulsing off of stop when cranking, not holding steady.

Verified fuel pump is operational and delivering plenty of pressure to injector pump low side feed. Validated fuel pressure/feed at the filter output line.
I was not able to get any high pressure output from the injector pumps even manipulating the solenoid/rail manually.
 

Ray70

Well-known member
2,595
5,912
113
Location
West greenwich/RI
Ok, sounds like a potential fuel rail / stuck Metering pump pin issue as far as no fuel out of the metering pumps
However it sounds like you still have some kind of DC voltage issue going on if you fuel stop solenoid is bouncing around.
CallMeColt just posted a fantastic video the other day showing how the fuel rack works as seen from inside the block.
Can you put a volt meter on your batteries or other 24V location and tell us what the voltage drops to while cranking?
I suspect you have at least 1 battery that is marginal at best, causing you to loose voltage while cranking.
Or better yet, do you happen to have a battery load tester? they are like $19 for a cheap one at Harbor Freight.
 

CallMeColt

Well-known member
Supporting Vendor
1,026
1,475
113
Location
Wilson County, Texas
Ok, sounds like a potential fuel rail / stuck Metering pump pin issue as far as no fuel out of the metering pumps
However it sounds like you still have some kind of DC voltage issue going on if you fuel stop solenoid is bouncing around.
CallMeColt just posted a fantastic video the other day showing how the fuel rack works as seen from inside the block.
Can you put a volt meter on your batteries or other 24V location and tell us what the voltage drops to while cranking?
I suspect you have at least 1 battery that is marginal at best, causing you to loose voltage while cranking.
Or better yet, do you happen to have a battery load tester? they are like $19 for a cheap one at Harbor Freight.
I just got this tester a few weeks ago and am happy with it for the cost. It does a few extra things over the $20 Harbor Freight one.
https://amzn.to/3Y3Mmyi
 

rcamacho

Well-known member
770
844
93
Location
Bainbridge Island Wa
Saw your video on the IP rail. Very helpful
I doubt the rail/governor is at fault as the assembly moves freely at the throttle and solenoid arms.

Thinking my next step is to remove and clean/inspect IP’s. Good opportunity to replace a seeping low pressure hose assembly.

DC is definitely low asI’ve been using the batteries a lot. I’ll recharge and see if the solenoid still acts up.


Sent from my iPhone using Tapatalk
 

CallMeColt

Well-known member
Supporting Vendor
1,026
1,475
113
Location
Wilson County, Texas
Saw your video on the IP rail. Very helpful
I doubt the rail/governor is at fault as the assembly moves freely at the throttle and solenoid arms.

Thinking my next step is to remove and clean/inspect IP’s. Good opportunity to replace a seeping low pressure hose assembly.

DC is definitely low asI’ve been using the batteries a lot. I’ll recharge and see if the solenoid still acts up.


Sent from my iPhone using Tapatalk
It may move freely because it is not moving the pump levers at it should. They may have "missed" the hole when installing. Have seen this the other way where the pumps "missed" the hole but were way beyond full throttle and you'd go to start it & it would scream until it died out of fuel in 20-30 seconds or so.

Inspect your injection pumps by removing them completely and going through the process of installing them as the TM says too. It will take an extra 5 minuets to check the rail inside with a light and mirror to be sure it is okay.

Then, once they are installed, try to start it for a while and look for fuel coming out of the top of the pumps before putting the lines back on to the injectors. This will purge your air out of the pumps as well.

Really sounds like your injection pumps are not installed properly and simply are not delivering fuel because of it. But, just reading and not being there isn't the whole story either. :)
 

Billy2642

Member
116
16
18
Location
Yakima, wa
After you verify your batteries are good and fully charged...

To help isolate the cause of the starter dropping out you could measure the DC voltage at relay K16 terminals 6 & 9 with respect to chassis ground.
Both terminals should have about 24 volts DC on them when cranking.
If both have 24 volts on them and them when the starter stops then issue may be with the K2 starter relay.
If you only have 24 volts on terminal 9 when the starter stops then issue may be with S14 or the MPU.
If you don't have any DC voltage on either terminal when the starter stops then issue may be with a fault being generated by the fault monitor.

Here are the terminal locations on all the relay sockets.
View attachment 885213
Here are the relay locations
View attachment 885214
off topic but do you have a similar picture of what each relay is for for the 804/5/6?
 