Sorry for the slow reply. Helping 4 people simultaneously with generator issues around the US this evening.
The START voltage signal comes from S1-7 and goes to TB5 terminal 14. In total terminal 14 will have 4 wires on it. Two on the top screw and two on the bottom screw.
The wire numbers for the 4 wires on TB5-14 are...
140A From S1-7
140B to K12-8 (feeds the Starter circuit)
140C to K15-A (feeds the Flashing circuit)
140D to the diagnostic connector on the outside top left.

Try disconnecting all wires from TB5-14. See if CB1 still pops.
If it doesn't then reconnect wire 140A to TB5-14 and see if CB1 pops.
If it doesn't then reconnect wire 140B to TB5-14 and see if CB1 pops.
If it doesn't reconnect wire 140C to TB5-14 and see if CB1 pops.
If it doesn't reconnect wire 140D to TB5-14 and see if CB1 pops.
 

jaybird67k

Active member
108
27
28
Location
Texas
The START voltage signal comes from S1-7 and goes to TB5 terminal 14. In total terminal 14 will have 4 wires on it. Two on the top screw and two on the bottom screw.
The wire numbers for the 4 wires on TB5-14 are...
140A From S1-7
140B to K12-8 (feeds the Starter circuit)
140C to K15-A (feeds the Flashing circuit)
140D to the diagnostic connector on the outside top left.

Try disconnecting all wires from TB5-14. See if CB1 still pops.
If it doesn't then reconnect wire 140A to TB5-14 and see if CB1 pops.
If it doesn't then reconnect wire 140B to TB5-14 and see if CB1 pops.
If it doesn't reconnect wire 140C to TB5-14 and see if CB1 pops.
If it doesn't reconnect wire 140D to TB5-14 and see if CB1 pops.
It will probably be Monday before I can fool with it since I'm busy tomorrow. Thanks Kloppk for the detailed instructions.
I'll keep you updated. Is there anyway I can get a moderator to change the thread title to cb1 instead of cb3 ?
 

jaybird67k

Active member
108
27
28
Location
Texas
Unplugged all wires from TB5 at 14 and it started normally. Hooked A up started hooked B up started hooked C up started hooked D up started with no CB1 pop.

All hooked up and CB1 didnt pop.
It's so intermittent. Why is it starting now.... Lol.
I'll try later when it heats up today outside.
 

jaybird67k

Active member
108
27
28
Location
Texas
I don't think it started with all four unplugged but started with A B C and D plugged in. May have gave some goofey info there.
I believe it just made a noise with all four unplugged but didnt pop CB1.
 

jaybird67k

Active member
108
27
28
Location
Texas
So after it sat in the sun for a bit went to start it and CB1 popped. So I did the wires again and this is what I get.
All four wires off= both solinoids click
A=both solinoids click
B= start
C=start
D= start

Now magically it's starting again 🥺
Frustrating.
 

jaybird67k

Active member
108
27
28
Location
Texas
Update !!!!
So I purchased a CB1 from eBay and installed it and it works fine now. So I took the old one apart by drilling out the rivets and sanding down the blob of sealant. Inside I found the contacts were corroded or burnt not making a good connection.
I cleaned both contacts on the old one and reassembled it and it also works fine now.
I have attached pictures from the inside of the old one. I only have one picture of a dirty contact because I cleaned one before I got a picture.

Thanks for all the help and I hope this helps someone in the future.
Also if someone can explain why dirty contacts would make it trip that would be awesome.
Reminded me of dirty points on a car engine that we used to have to clean.
 

Attachments